    Problem with chiller



    We are using HITACHI Chiller, Model No.: RCUP-46AU(Z). Refrigerent R 407 C.
    Our main problem is the chiller section sometimes tripped and fault shows 13-13 Active of freeze protection by thermistr.
    #Chilled water inlet temp. 10 Deg. C and outlet temp. 9 Deg. C.
    #We check the thirmistor.
    # Chilled water flow pressure is ok, and we also clean the evaporator (as described in manual) after the problem arrived.
    # Purge air from the chilled water line.
    Note: After cleaning the evaporator the chiller unit didnt tripped for a week, and after that it showing the same problem again.
    What is the probable troubleshooting steps now...............?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Problem with chiller

    You say that the chilled water flow pressure is OK but is the flow rate correct?

    Also you are only showing 1°C across the evaporator, not very much happening there is there?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2010
    Location
    Bangladesh
    Age
    40
    Posts
    151
    Rep Power
    15

    Re: Problem with chiller

    Sir,
    Thanks for the replay..........
    I have no idea how to measure flow rate across the evaporator, & most of the time chilled water inlet & outlet temperature difference is not less then 2 deg C.

  4. #4
    Join Date
    Mar 2010
    Location
    Dammam
    Posts
    83
    Rep Power
    15

    Re: Problem with chiller

    this is unusual,temp. difference across the evaporator should be around 6-9 deg. Celsius.,Brian_UK is correct,check the chilled water flowrate,maybe you dont have enough water velocity in the evaporator.,or there is ice-build up in the evaporator coils,check also your expansion valve.

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Problem with chiller

    I would start with the piping. The water should enter the bottom of the evaporator and exit the top.

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Problem with chiller

    Quote Originally Posted by Bashir01219 View Post
    We are using HITACHI Chiller, Model No.: RCUP-46AU(Z). Refrigerent R 407 C.
    Our main problem is the chiller section sometimes tripped and fault shows 13-13 Active of freeze protection by thermistr.
    #Chilled water inlet temp. 10 Deg. C and outlet temp. 9 Deg. C.
    #We check the thirmistor.
    # Chilled water flow pressure is ok, and we also clean the evaporator (as described in manual) after the problem arrived.
    # Purge air from the chilled water line.
    Note: After cleaning the evaporator the chiller unit didnt tripped for a week, and after that it showing the same problem again.
    What is the probable troubleshooting steps now...............?
    Was there air in the chilled water line?

  7. #7
    Join Date
    Mar 2010
    Location
    Bangladesh
    Age
    40
    Posts
    151
    Rep Power
    15

    Re: Problem with chiller

    The water should enter the bottom of the evaporator and exit the top. Yes our chilled water system line have the facility.

  8. #8
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Problem with chiller

    hi bashir, also is the chiller very old?, have you inspected the chilled water strainer?

  9. #9
    Join Date
    Mar 2010
    Location
    Bangladesh
    Age
    40
    Posts
    151
    Rep Power
    15

    Re: Problem with chiller

    we have strainer after pump but not before evaporator.

  10. #10
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Problem with chiller

    Quote Originally Posted by ref717 View Post
    t...temp. difference across the evaporator should be around 6-9 deg. Celsius.,Brian_UK is correct,check the chilled water flowrate,maybe you dont have enough water velocity in the evaporator....
    If you should have not enough waterflow,then you will see a big DT,
    So in his case, waterflow is extremely high
    Where is freeze protection measurement located exactly?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  11. #11
    Join Date
    Mar 2010
    Location
    Bangladesh
    Age
    40
    Posts
    151
    Rep Power
    15

    Re: Problem with chiller

    How can we measure water flow? We can measure it through raw method, but is it error free.
    Parallel we have another Trane chiller, and there is no problem.
    And the position of the freeze protection sensor is chilled water outlet line.

  12. #12
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Problem with chiller

    Quote Originally Posted by Peter_1 View Post
    If you should have not enough waterflow,then you will see a big DT,
    So in his case, waterflow is extremely high
    Where is freeze protection measurement located exactly?
    Unless there is zero waterflow, in which case there should be zero dT.

  13. #13
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Problem with chiller

    Quote Originally Posted by Gary View Post
    Was there air in the chilled water line?
    You missed this question.

  14. #14
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Problem with chiller

    Quote Originally Posted by Bashir01219 View Post
    Chilled water flow pressure is ok...
    Ok is an opinion, not a pressure.

    What is the pressure?

  15. #15
    Join Date
    Mar 2010
    Location
    Bangladesh
    Age
    40
    Posts
    151
    Rep Power
    15

    Re: Problem with chiller

    Chilled water inlet pressure 4.8 Bar, & outlet pressure nearly 4.0 Bar.
    There is no air in the chilled water line, we check the air venting line several times.
    sometimes dT shows Zero, at the begining of the machine start.

  16. #16
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,554
    Rep Power
    26

    Re: Problem with chiller

    Hi, do you know what your suction pressure/temp.
    Are you sure that the freeze sensor is in the water line, and not in a pocket in the evap.
    My gut feeling is that your tubes are fouled, stopping heat transfer, but not enough to block the flow. causing a lower SST than normal
    Mad F
    Last edited by mad fridgie; 12-04-2010 at 03:35 AM.

  17. #17
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Problem with chiller

    What refrigerant is in the system?

    When the system is running, what are the pressures, temperatures, subcooling, superheat?

    When the system is off what pressure does it equalize at?

  18. #18
    Join Date
    Mar 2010
    Location
    Bangladesh
    Age
    40
    Posts
    151
    Rep Power
    15

    Re: Problem with chiller

    Sir, Lots of question?
    You know i am new in this line,

    Refrigerant: R407C,
    System need to run at 7.00 am to 8.00 pm (everyday).
    Temp. at TXV valve 17 deg C, Evaporating pressure 95 PSI
    Superheat temp. nearly 6 deg C.
    Compresser discharge pressure 340 PSI,
    Temperature leaving the condenser 53.1 deg C
    So, subcool temp. 3 deg C.
    Note: Parallel we have another Trane chiller.

  19. #19
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,554
    Rep Power
    26

    Re: Problem with chiller

    Quote Originally Posted by Bashir01219 View Post
    Sir, Lots of question?
    You know i am new in this line,

    Refrigerant: R407C,
    System need to run at 7.00 am to 8.00 pm (everyday).
    Temp. at TXV valve 17 deg C, Evaporating pressure 95 PSI
    Superheat temp. nearly 6 deg C.
    Compresser discharge pressure 340 PSI,
    Temperature leaving the condenser 53.1 deg C
    So, subcool temp. 3 deg C.
    Note: Parallel we have another Trane chiller.
    Good info, based upon this your water temp readings are wrong, your evap temp is higher than your water temp.

  20. #20
    Join Date
    Mar 2010
    Location
    Bangladesh
    Age
    40
    Posts
    151
    Rep Power
    15

    Re: Problem with chiller

    when i got the readings, chilled water temp. was in inlet 15 deg. C, & outlet 14 deg. C.

  21. #21
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Problem with chiller

    Quote Originally Posted by Bashir01219 View Post
    when i got the readings, chilled water temp. was in inlet 15 deg. C, & outlet 14 deg. C.
    Your readings are still wrong. What are you measuring temperatures with?

  22. #22
    Join Date
    Mar 2010
    Location
    Bangladesh
    Age
    40
    Posts
    151
    Rep Power
    15

    Re: Problem with chiller

    From the panel i got the temp.

Similar Threads

  1. problem with multistack chiller
    By bright in forum Refrigerants
    Replies: 3
    Last Post: 30-10-2010, 10:43 PM
  2. Problem with mcquay chiller
    By texanul in forum Industrial
    Replies: 6
    Last Post: 04-02-2010, 08:51 PM
  3. Problem with centrifugal chiller
    By engalmohannad in forum Commercial
    Replies: 0
    Last Post: 19-04-2009, 10:00 PM
  4. York YK Chiller Problem
    By icebox in forum Refrigeration Books
    Replies: 13
    Last Post: 01-07-2008, 06:05 PM
  5. Chiller tripping Problem
    By bhasadu in forum Trouble Shooting
    Replies: 0
    Last Post: 21-06-2008, 09:12 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •