07-04-2010, 10:31 AM #1
Problem with chiller
We are using HITACHI Chiller, Model No.: RCUP-46AU(Z). Refrigerent R 407 C.
Our main problem is the chiller section sometimes tripped and fault shows 13-13 Active of freeze protection by thermistr.
#Chilled water inlet temp. 10 Deg. C and outlet temp. 9 Deg. C.
#We check the thirmistor.
# Chilled water flow pressure is ok, and we also clean the evaporator (as described in manual) after the problem arrived.
# Purge air from the chilled water line.
Note: After cleaning the evaporator the chiller unit didnt tripped for a week, and after that it showing the same problem again.
What is the probable troubleshooting steps now...............?
-
07-04-2010, 11:24 PM #2
Re: Problem with chiller
You say that the chilled water flow pressure is OK but is the flow rate correct?
Also you are only showing 1°C across the evaporator, not very much happening there is there?Brian - Newton Abbot, Devon, UK
Retired March 2015
-
08-04-2010, 03:17 AM #3
Re: Problem with chiller
Sir,
Thanks for the replay..........
I have no idea how to measure flow rate across the evaporator, & most of the time chilled water inlet & outlet temperature difference is not less then 2 deg C.
-
08-04-2010, 04:46 PM #4
Re: Problem with chiller
this is unusual,temp. difference across the evaporator should be around 6-9 deg. Celsius.,Brian_UK is correct,check the chilled water flowrate,maybe you dont have enough water velocity in the evaporator.,or there is ice-build up in the evaporator coils,check also your expansion valve.
-
08-04-2010, 05:00 PM #5
Re: Problem with chiller
I would start with the piping. The water should enter the bottom of the evaporator and exit the top.
-
08-04-2010, 05:02 PM #6
Re: Problem with chiller
-
09-04-2010, 06:41 AM #7
Re: Problem with chiller
The water should enter the bottom of the evaporator and exit the top. Yes our chilled water system line have the facility.
-
09-04-2010, 03:51 PM #8
Re: Problem with chiller
hi bashir, also is the chiller very old?, have you inspected the chilled water strainer?
-
10-04-2010, 03:17 AM #9
Re: Problem with chiller
we have strainer after pump but not before evaporator.
-
11-04-2010, 09:00 AM #10
Re: Problem with chiller
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
11-04-2010, 10:25 AM #11
Re: Problem with chiller
How can we measure water flow? We can measure it through raw method, but is it error free.
Parallel we have another Trane chiller, and there is no problem.
And the position of the freeze protection sensor is chilled water outlet line.
-
11-04-2010, 02:48 PM #12
Re: Problem with chiller
-
11-04-2010, 02:49 PM #13
Re: Problem with chiller
-
11-04-2010, 02:52 PM #14
Re: Problem with chiller
-
12-04-2010, 03:18 AM #15
Re: Problem with chiller
Chilled water inlet pressure 4.8 Bar, & outlet pressure nearly 4.0 Bar.
There is no air in the chilled water line, we check the air venting line several times.
sometimes dT shows Zero, at the begining of the machine start.
-
12-04-2010, 03:33 AM #16
Re: Problem with chiller
Hi, do you know what your suction pressure/temp.
Are you sure that the freeze sensor is in the water line, and not in a pocket in the evap.
My gut feeling is that your tubes are fouled, stopping heat transfer, but not enough to block the flow. causing a lower SST than normal
Mad FLast edited by mad fridgie; 12-04-2010 at 03:35 AM.
-
12-04-2010, 03:39 AM #17
Re: Problem with chiller
What refrigerant is in the system?
When the system is running, what are the pressures, temperatures, subcooling, superheat?
When the system is off what pressure does it equalize at?
-
12-04-2010, 04:14 AM #18
Re: Problem with chiller
Sir, Lots of question?
You know i am new in this line,
Refrigerant: R407C,
System need to run at 7.00 am to 8.00 pm (everyday).
Temp. at TXV valve 17 deg C, Evaporating pressure 95 PSI
Superheat temp. nearly 6 deg C.
Compresser discharge pressure 340 PSI,
Temperature leaving the condenser 53.1 deg C
So, subcool temp. 3 deg C.
Note: Parallel we have another Trane chiller.
-
12-04-2010, 04:35 AM #19
-
12-04-2010, 05:41 AM #20
Re: Problem with chiller
when i got the readings, chilled water temp. was in inlet 15 deg. C, & outlet 14 deg. C.
-
12-04-2010, 06:12 AM #21
Re: Problem with chiller
-
12-04-2010, 07:01 AM #22
Re: Problem with chiller
From the panel i got the temp.
Similar Threads
-
problem with multistack chiller
By bright in forum RefrigerantsReplies: 3Last Post: 30-10-2010, 10:43 PM -
Problem with mcquay chiller
By texanul in forum IndustrialReplies: 6Last Post: 04-02-2010, 08:51 PM -
Problem with centrifugal chiller
By engalmohannad in forum CommercialReplies: 0Last Post: 19-04-2009, 10:00 PM -
York YK Chiller Problem
By icebox in forum Refrigeration BooksReplies: 13Last Post: 01-07-2008, 06:05 PM -
Chiller tripping Problem
By bhasadu in forum Trouble ShootingReplies: 0Last Post: 21-06-2008, 09:12 AM