    Shell and Tube service life



    I've got a pair of ONDA shell and tube heat exchangers used to chill a calcium chloride brine solution to approximately -35°C

    What is the expected service life of of such a system?

    Are there any steps that can be take to extend the useful life?



  2. #2
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Shell and Tube service life

    Provided you maintain your CaCl2 charge with the proper inhibitors, and the exchanger was designed properly, no reason not to get 20 years plus from the exchanger.

    Ken

  3. #3
    Join Date
    Apr 2008
    Location
    canada
    Age
    75
    Posts
    94
    Rep Power
    17

    Re: Shell and Tube service life

    B”H

    What is the concentration of calcium chloride to be able to reach -35C.

  4. #4
    Join Date
    Apr 2007
    Location
    United States
    Posts
    51
    Rep Power
    18

    Re: Shell and Tube service life

    Quote Originally Posted by michaelm View Post
    B”H

    What is the concentration of calcium chloride to be able to reach -35C.
    We target a concentration of 1.28 to 1.29.

    Someone pushed the concentration to 1.34 the other day thinking more must be better and just about make the whole issue moot by freezing the entire system solid.

    Quote Originally Posted by TXiceman
    B”H

    Provided you maintain your CaCl2 charge with the proper inhibitors, and the exchanger was designed properly, no reason not to get 20 years plus from the exchanger.
    Can you suggest a proper inhibitor? I'm very sure my systems have never seen any type of care or use of any inhibitors.

  5. #5
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Shell and Tube service life

    Probably the correct ph as well .

  6. #6
    Join Date
    Nov 2004
    Location
    China
    Posts
    176
    Rep Power
    20

    Re: Shell and Tube service life

    Try Brinehib from Ashland Chemicals. ( I don't think it's food approved)
    Keep the heat exchanger full of brine. If it gets exposed to air by draining the system or similar action, the tubes won't last more than a few weeks.
    Minimize turbulence if you have an open system. you don't want excess oxygen in the brine.

Similar Threads

  1. Replies: 2
    Last Post: 08-06-2010, 11:12 PM
  2. Fabrication of Cooler Tube & Shell Cooler
    By rickyccong in forum Technical Discussions
    Replies: 1
    Last Post: 27-07-2009, 02:25 PM
  3. Water velocity in Shell and tube HE
    By wilsoncheung in forum Industrial
    Replies: 15
    Last Post: 07-04-2009, 07:59 PM
  4. Replies: 3
    Last Post: 09-09-2008, 04:33 AM
  5. Help!!! Shell and Tube Evap Leak
    By tommy Gun in forum Trouble Shooting
    Replies: 7
    Last Post: 22-07-2007, 12:45 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •