    Inconsistant KF Water from R134A

    We have been getting varied results from performing KF Water on samples from two Refrigeration Turbine Type Compressors.
    These two compressors are running Castrol Icematic 68 with the gas being R134a, Tetrafluoroethane (CF3CH2F) from the family of HFC refrigerants.

    KF Water performed on other machines appear correct and as expected with the difficulty only appearing with these two compressors.

    We have split samples between the two labs and gathered results from other samples processed from the two compressors at the same labs.

    As we can see from the results tabulated in the chart both Labs have low and elevated results, note when we split samples with dry bottles we received dissimilar results.
    Note how when the lab manager double checked the results on the 18th of November that the individual lab process’s delivered similar results as expected.

    As you would understand these two compressors are a sealed system operating at approximately 100 PSI and there should be no opportunity for environmental contaminates to gain entry and we have been monitoring these compressors by microscope for 6-7 years and at present the two compressors appear to be running in a normal wear mode at a low rate of wear with a low level fine hard particle abrasive wear debris evident but no indication of oil gelling or water damaged lubricant agglomerations in the samples.

    The only variable we can think of is if the R134a, Tetrafluoroethane (CF3CH2F) refrigerant is affecting the titration process and the amount of gas remaining in the sample is the variable as the sample temperature and length of time standing would change the amount of residual gas remaining.

    We need to figure why we are getting the varied results as when we go over 100 ppm water a $10,000 system dry out and oil change is recommended for the compressor and at present we have invested > 8 hours of R&T lab time, 6 hours of site time and > $500 of KF Water analysis and have no results that we are confident in enough to hand onto our customer.


    Thanks for your assistance with this.


    Best Regards





    Rob S
    Attached Files Attached Files

Similar Threads

  1. Fact or Fiction
    By david.findlay in forum Fundamentals
    Replies: 40
    Last Post: 09-03-2009, 06:19 PM
  2. Modifying aricond. for heating, cooling and hot water
    By kimusabi in forum Technical Discussions
    Replies: 3
    Last Post: 10-10-2008, 07:28 AM
  3. R134a / Water Heat Exchanger Sizing
    By ACEprod in forum CPU Overclockers
    Replies: 0
    Last Post: 31-03-2008, 07:34 AM
  4. open cycle R718 A/C that also provides high purity water?
    By star882 in forum Technical Speculations
    Replies: 7
    Last Post: 27-07-2006, 04:18 AM
  5. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •