    commercial walk in freezer qestion



    walkin has ten fans . compressor in separate room. Should fans push or pull the air? no one seems to be sure.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: commercial walk in freezer qestion

    They generally pull the air as it reduces the jetting affect on the coil face.

    Also the cowling around the fan blade encourages the air to be 'thrown' further.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: commercial walk in freezer qestion

    Are you asking because your fans are pushing?

    About 16 or more years ago Witt redesigned their low profile unit coolers to push the air. The fan motors were on the back and the coil was in the front.

    The theory was that the cabinet would act as a pressurized plenum and the air would distribute evenly and efficiently and have a longer air throw.

    The problem was; some were installed backwards due to misunderstandings of the design and if a filter sock wasn't installed on the fan motor guards the coil would clog up and they were a PIA to clean.

    Witt eventually converted back to the pull thru design.
    Thousands of HVACR manufacturers links! Visit: www.hvacrinfo.com

  4. #4
    Join Date
    Jul 2008
    Location
    birmingham
    Age
    39
    Posts
    23
    Rep Power
    0

    Re: commercial walk in freezer qestion

    most systems that i work on pull the air across the coil, what type of evaporator is it?

  5. #5
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: commercial walk in freezer qestion

    Quote Originally Posted by cborel View Post
    walkin has ten fans . compressor in separate room. Should fans push or pull the air? no one seems to be sure.
    Hi Many years ago the fans used to push air through now the protocol has changed to draw through
    My wife used to say you never listen to a word I say at least I think that what she said

  6. #6
    Join Date
    Apr 2010
    Location
    us
    Posts
    5
    Rep Power
    0

    Re: commercial walk in freezer qestion

    It is a Russell evaporator. The coils are positioned behind slightly above the fans. The coils appear slightly cleaner in the set of fans that are pulling the air from the freezer up through the coil area..obviously i know little about this. But also the question needs to be answered as to whether all fans should go the same direction..

  7. #7
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: commercial walk in freezer qestion

    It doesn't matter, its the design of the evaporator.

    In some they pull the air and some they push.

  8. #8
    Join Date
    Apr 2010
    Location
    us
    Posts
    5
    Rep Power
    0

    Re: commercial walk in freezer qestion

    Also, while I have your intelligence working for me...can you replumb the defrosting copper lines with another product..meaning the plastic used today.

  9. #9
    Monty1987's Avatar
    Monty1987 Guest

    Re: commercial walk in freezer qestion

    hey mate, as far as i know but then i might be wrong or right this is what i think though. normally most of the coil fans suck air from alliminium fins side and distributes air from the fan side, it all depends what type of the evapoutor you dealing with. best way to check is the direction of the fan blade and which way its blowing. so then the evap should be sucking and blowing through the fans, and all fans should be going in one way.

  10. #10
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: commercial walk in freezer qestion

    Tech terms
    Forced Draft (blow)= Air In - Fan - Coil- Air Out
    Induced Draft (suck) Air In - Coil - Fan - Air Out.
    Both are acceptable, Induced draft, normally gives greater "air throw in free air" blows further.
    When working with multiple fans all should be moving air in the same direction.
    Yes can run drains in plastic, but if you need a heat tape, make sure plastic is high temp rated or the heat tape is temperature limited

  11. #11
    Join Date
    Apr 2010
    Location
    us
    Posts
    5
    Rep Power
    0

    Re: commercial walk in freezer qestion

    Thank you very much ...the last post was extremely helpful...

  12. #12
    Join Date
    Apr 2010
    Location
    us
    Posts
    5
    Rep Power
    0

    Re: commercial walk in freezer qestion

    new problem...now the fans are corrected but they run continuously even in the defrost cycle...what has caused this...

Similar Threads

  1. walk in freezer
    By ail in forum Refrigerants
    Replies: 8
    Last Post: 29-11-2009, 11:44 PM
  2. help!! getting beat up by a walk in freezer
    By avalanche in forum Commercial
    Replies: 12
    Last Post: 05-12-2008, 02:56 AM
  3. superheating 5-8 dc right for walk in freezer r404
    By przemo2 in forum Technical Speculations
    Replies: 3
    Last Post: 09-03-2008, 01:56 PM
  4. walk in freezer refrigeration sizing?
    By trammd in forum Technical Discussions
    Replies: 10
    Last Post: 02-11-2006, 11:56 AM
  5. It's snowing in my walk in freezer!
    By Matt in forum Commercial
    Replies: 19
    Last Post: 14-10-2006, 07:07 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •