    Dears,
    Could you pls kindly help me to find out the root of cause of one problem.We are installing the 100000 CMH,axial fan for engine room in one of the ship.The spec of the fan is as follow,
    Capacity 100000 CMH
    SP 400 pa
    Elec 440V/3ph/60 HZ
    Power 45 KW
    Cavity 16
    Blades 12
    Material Aluminium alloy
    RPM 1750
    There is a problem that we have to change the impeller more thn a dozen of times since the impeller is keep on breaking like once a month.The bottom of the fan ,there is a foundation and after that there is a structural chamber,all together total 1600 mm.The fan dia is 1120.
    Thanks for ur interest in this thread and looking for ur advise and comments.
    Mar 2009
    KZN, South Africa
    64
    2,212
    Re: Ventilation Fan
    I suggest you take some pictures of the fan failures & post them up for comment.
    Aluminium alloys will suffer in a fatigue environment, especially if geometric stress-raisers exist, or excessive porosity.
    Aug 2009
    New Zealand
    2,554
    26
    Re: Ventilation Fan
    Thats moving at a fair few "Knots"
    Are you building the fan up yourselves.
    Fitting the 12 blades to the hub? If so you are likely making with an inbalance. (causing a lot of stress)
    I would suggest you have these built by a specialist and have it balanced.
    Similar to what is done on a car wheel!
    Sep 2003
    ISRAEL
    72
    4,248
    Re: Ventilation Fan
    you should use a belt driven fan or centrifugal fan, much less stress on the motor and blades
    Feb 2008
    adelaide sth.oz
    1,015
    Re: Ventilation Fan
    increase the number of blades and reduce the pitch or as above
    11,025
    Re: Ventilation Fan
    Check that there is a good screen in front of the fan, there may be foreign matter getting sucked through and hitting the blades.
    Auckland
    74
    3,357
    37
    Re: Ventilation Fan
    If I read it correctly you have a case diameter of 1600mm and a fan diameter of 1120mm, at the high volume rate and static pressure of 400pa, you will get very high slippage, off the end of blades creating buffeting/ pulsing. This will flex the blades and create metal fatigue and broken blades.
    Aug 2007
    Sydney
    52
    1,083
    23
    Re: Ventilation Fan
    Yes as mad fridgie suggests check for imballance. Also check for harmonic resonance or cavitation. you could take basic measurement with a scope and sensitive mic but probably an engineer would need to analyse. But on a quick calculation from your specs it does'nt add up - can you provide some fan curves or possiby contact the manufacturer for more data? and measure pressure differential across the fan
    Mar 2010
    Dammam
    83
    15
    Re: Ventilation Fan
    This fan blade falure is a complicated issue. You need to first investigate where is the fracture surface and analyze if it was fatigue failure or material failure?. Anyway, above comments are correct.,you may have an inbalanced fan blade or
    aerodynamic disturbance that resulted in resonant vibration.
    Mar 2010
    Vietnam
    Re: Ventilation Fan
    Dears,
    Thanks for ur valuable comments,we checked the balancing and found that is out 0.05 mm only.And for the material,the casting seems is not so bad that mean we cant find the air sac in the section of the impeller.And we cover the fan with the 12x12 x GA 16 wiremesh with reinforcement.So probably the is nothing to come and touch the impeller.We now suspect that because of the back pressure.Since the discharge side is only 1D of the fan and suction side is too.Now we install the guidevane at the discharge side and have to see the result.