    Ventilation Fan



    Dears,
    Could you pls kindly help me to find out the root of cause of one problem.We are installing the 100000 CMH,axial fan for engine room in one of the ship.The spec of the fan is as follow,
    Capacity 100000 CMH
    SP 400 pa
    Elec 440V/3ph/60 HZ
    Power 45 KW
    Cavity 16
    Blades 12
    Material Aluminium alloy
    RPM 1750

    There is a problem that we have to change the impeller more thn a dozen of times since the impeller is keep on breaking like once a month.The bottom of the fan ,there is a foundation and after that there is a structural chamber,all together total 1600 mm.The fan dia is 1120.
    Thanks for ur interest in this thread and looking for ur advise and comments.



  2. #2
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Ventilation Fan

    I suggest you take some pictures of the fan failures & post them up for comment.

    Aluminium alloys will suffer in a fatigue environment, especially if geometric stress-raisers exist, or excessive porosity.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  3. #3
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Ventilation Fan

    Thats moving at a fair few "Knots"
    Are you building the fan up yourselves.
    Fitting the 12 blades to the hub? If so you are likely making with an inbalance. (causing a lot of stress)
    I would suggest you have these built by a specialist and have it balanced.
    Similar to what is done on a car wheel!

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Ventilation Fan

    you should use a belt driven fan or centrifugal fan, much less stress on the motor and blades

  5. #5
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Ventilation Fan

    increase the number of blades and reduce the pitch or as above
    mmm to beer or not to beer...........lets drink breakfast

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Ventilation Fan

    Check that there is a good screen in front of the fan, there may be foreign matter getting sucked through and hitting the blades.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Ventilation Fan

    If I read it correctly you have a case diameter of 1600mm and a fan diameter of 1120mm, at the high volume rate and static pressure of 400pa, you will get very high slippage, off the end of blades creating buffeting/ pulsing. This will flex the blades and create metal fatigue and broken blades.

  8. #8
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,083
    Rep Power
    23

    Re: Ventilation Fan

    Yes as mad fridgie suggests check for imballance. Also check for harmonic resonance or cavitation. you could take basic measurement with a scope and sensitive mic but probably an engineer would need to analyse. But on a quick calculation from your specs it does'nt add up - can you provide some fan curves or possiby contact the manufacturer for more data? and measure pressure differential across the fan

  9. #9
    Join Date
    Mar 2010
    Location
    Dammam
    Posts
    83
    Rep Power
    15

    Re: Ventilation Fan

    This fan blade falure is a complicated issue. You need to first investigate where is the fracture surface and analyze if it was fatigue failure or material failure?. Anyway, above comments are correct.,you may have an inbalanced fan blade or
    aerodynamic disturbance that resulted in resonant vibration.

  10. #10
    Join Date
    Mar 2010
    Location
    Vietnam
    Age
    39
    Posts
    25
    Rep Power
    0

    Re: Ventilation Fan

    Dears,
    Thanks for ur valuable comments,we checked the balancing and found that is out 0.05 mm only.And for the material,the casting seems is not so bad that mean we cant find the air sac in the section of the impeller.And we cover the fan with the 12x12 x GA 16 wiremesh with reinforcement.So probably the is nothing to come and touch the impeller.We now suspect that because of the back pressure.Since the discharge side is only 1D of the fan and suction side is too.Now we install the guidevane at the discharge side and have to see the result.
    Regards
    Aung

Similar Threads

  1. Industrial ventilation design guide
    By vijay_study in forum Air Conditioning
    Replies: 5
    Last Post: 10-12-2008, 06:46 PM
  2. CO monitor controlled ventilation
    By Rabindra in forum Air Conditioning
    Replies: 2
    Last Post: 29-11-2007, 04:09 PM
  3. Ventilation
    By SteveDixey in forum Air Conditioning
    Replies: 2
    Last Post: 24-09-2007, 11:40 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •