Results 1 to 2 of 2
Thread: Frick compressor TDSH193
-
01-04-2010, 03:08 PM #1
Frick compressor TDSH193
Good Morning,
I was on line looking for a TDSH193 Repair manual and found several on this site asking for the same thing. I have the parts Manual and that is easy to find on line. The actual repair manual, not so easy. If anyone knows how I can get one, point me in the right direction or can send me one that would be great. andymartin540@gmail.com.
I have a second question; What is considered A high DP for the oil filter. Running dual filters and can switch.
Thank you for any information in advance. Andy
-
01-04-2010, 04:57 PM #2
Re: Frick compressor TDSH193
Hi, Andy
Hard to say but the best is to switch when you reach 0,8 - 1 bar max (14PSI) or earlier ... take in consideration what is your actual oil pressure to not trigger oil safety pressure switch..
The good maintenance is to switch over at 0,5 bar and clean the dirty one no need to force anything ...
Best regards, Josip
It's impossible to make anything foolproof because fools are so ingenious...
Don't ever underestimate the power of stupid people when they are in large groups.
Please, don't teach me how to be stupid....
No job is as important as to jeopardize the safety of you or those that you work with.
Similar Threads
-
Frick suction check failure
By CanadianIce in forum Industrial CompressorsReplies: 4Last Post: 08-04-2010, 11:43 AM -
Frick TDSH 355 oil press. problems
By SQUATCH1 in forum Industrial CompressorsReplies: 5Last Post: 15-03-2010, 05:16 AM -
problem with volume on frick screw compressor
By samlee12 in forum IndustrialReplies: 4Last Post: 29-10-2009, 06:06 AM -
problem with frick screw volume
By samlee12 in forum Industrial CompressorsReplies: 9Last Post: 20-06-2009, 02:46 PM -
Ammonia Circulation rate - by Frick/ Vitler
By smpsmp45 in forum NH3Replies: 12Last Post: 16-06-2008, 10:06 AM