    daikin vrv 3 28 kw cap



    hi lads, can you give your views on a mini vrv 3 on r410a.
    need to re-locate an indoor unit on daikin vrv3 S/N RXYQ10P7W1B 28 kw capacity cooling.
    it will only move 2- 3 metes, which is best method, pump down or reclaim?
    for pump down any special advise or proceedure.
    best regards
    sork
    Last edited by sork; 01-04-2010 at 01:04 PM.



  2. #2
    Join Date
    Aug 2009
    Location
    Turhona.libya
    Posts
    79
    Rep Power
    15

    Re: daikin vrv 3 28 kw cap

    I would briefer reclaiming the refrigerant to pump down. i know it is a long method comparing to pump down but it is reliable and time saving in the cases of service valve passing

  3. #3
    Join Date
    Jun 2008
    Location
    london
    Age
    63
    Posts
    115
    Rep Power
    16

    Re: daikin vrv 3 28 kw cap

    thanks mate,but i do not need to add any refrigerant, it is not the master unit.

  4. #4
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: daikin vrv 3 28 kw cap

    hi , can you not get someone in to do a propper job? if you havent got the confidence or the experiance , how are you going to do the job properly?

  5. #5
    Join Date
    Jun 2008
    Location
    london
    Age
    63
    Posts
    115
    Rep Power
    16

    Re: daikin vrv 3 28 kw cap

    thanks for your advise, very helpful

  6. #6
    Join Date
    Jun 2008
    Location
    london
    Age
    63
    Posts
    115
    Rep Power
    16

    Re: daikin vrv 3 28 kw cap

    ok in some units there is a proceedure in which automatically ref will be parked and then you front seat vales, rather than lp switch and manual pump down. that was the question?

  7. #7
    Join Date
    Mar 2010
    Location
    England
    Posts
    41
    Rep Power
    0

    Re: daikin vrv 3 28 kw cap

    The system should be fully recovered. No VRV 3 system can be pumped down without risk of damage to the compressors. Set "Refrigerant Recovery Mode". Mode binary 21 to open all valves within indoor and outdoor unit and leave power on until fully recovered.

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. Daikin, Why do we bother?
    By gwilliamson in forum Air Conditioning
    Replies: 21
    Last Post: 02-02-2010, 09:38 AM
  3. Daikin FDYQ250M
    By carl in forum Air Conditioning
    Replies: 7
    Last Post: 11-08-2009, 12:56 AM
  4. Daikin AC parts from UK
    By skel00 in forum Air Conditioning
    Replies: 5
    Last Post: 05-04-2009, 01:24 PM
  5. Fixing Daikin A3 Error
    By Stuffy in forum Air Conditioning
    Replies: 3
    Last Post: 27-03-2009, 06:02 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •