Results 1 to 15 of 15
    Mar 2010
    Bahrain
    44
    Carrier Chiller 30XA1202 Alarm
    dears,
    i've an alarm in the panel of my Carrier Chiller model : 30XA1202 which reads ( electrical box interlock or electrical thermostat failure) and as a result the chiller does not start.
    please advise what action to be done?
    Apr 2009
    israel
    778
    Re: Carrier Chiller 30XA1202 Alarm
    Hi is there a number associated with this alarm ??
    Oct 2009
    merida mexico
    282
    Alarm 66 — Electrical Box Thermostat Failure/Reverse
    Rotation (P.28)
    NOTE: Alarm 66 is not used or supported. If this condition is
    encountered, confirm machine configuration.
    moideen's Avatar
    Apr 2008
    u.a.e
    49
    412
    Thumbs up Re: Carrier Chiller 30XA1202 Alarm
    Quote Originally Posted by Aqeelhassan View Post
    dears,
    this alarm related to flow switch.check the flow switch.
    moideen-dubai
    4,698
    I don't know if it Helps but the manual I have say's this -
    Control box poorly ventilated
    or poor electrical connection
    Good Luck Grizzly
    Jul 2003
    caribbean
    8
    have you checked the phasing on the incoming power to see if it has changed from the original configuration?
    Nov 2005
    Ireland
    As in the last post, check your phases and also that another unit is not been fed from the same power supply causing a voltage imbalanced.
    We had the same problem where on start-up; the customer was using a generator to give a temporary power supply to the chiller. In the building if the elevator motor turned on it would cause a slight drop in power and the chiller would trip on the same alarm.
    Sep 2008
    Newcastle upon tyne
    75
    80
    hello
    had same problem recently and its the built in flow switch check flows
    aww
    Oct 2009
    merida mexico
    282
    when the flow switch failure shows a lack of coolant flow
    Mar 2010
    Bahrain
    44
    Quote Originally Posted by goshen View Post
    no,there is no number in alarm
    sheffield
    10
    this is a flow switch fault,check your water flow
    Apr 2009
    israel
    778
    Quote Originally Posted by oldschooleng View Post
    Hi :
    after 3 weeks i would hope he relized as said before ,that it is the flow switch!!!
    gggraj's Avatar
    gggraj Guest
    hi im raj i have problem 30gx267 chiller. power off the through control switch for maintanace.then 4days after i turn on control switch i getting alaram 31 and 19 scpm board not responding what is the reason any body help me?scpm board led red light blinking and green light not blinking
    Oct 2009
    merida mexico
    282
    07 30 Circuit A Reclaim Pumpdown
    Pressure Transducer
    Measured voltage is
    0 vdc or SST > EWT and
    EXV < 50
    % for 1 minute
    None Automatic Configuration error
    08 31 Circuit B Reclaim Pumpdown
    Pressure Transducer
    Oct 2009
    merida mexico
    282
    21 19 Space Temperature
    Thermistor
    Temperature measured
    by the controller is
    outside of the range
    of –40 F to 245 F
    Alarm tripped Automatic Faulty Sensor, wiring
    error, failed EMM
    board
  1. Replies: 12
  2. Dunham Bush Chiller Alarm
    By Regulator in forum Air Conditioning
    Last Post: 08-12-2010, 01:42 AM
  3. Carrier chiller basic board problem
    By noushad123 in forum Trouble Shooting
    Last Post: 17-06-2010, 06:55 AM
  4. Carrier Chiller Help
    By superswill in forum Trouble Shooting
    Last Post: 18-01-2007, 10:06 PM
  5. Carrier chiller oil migration
    By lowtech in forum Industrial
    Last Post: 30-04-2006, 04:11 PM