dears,
i've an alarm in the panel of my Carrier Chiller model : 30XA1202 which reads ( electrical box interlock or electrical thermostat failure) and as a result the chiller does not start.
please advise what action to be done?
30-03-2010, 07:02 PM #2
Re: Carrier Chiller 30XA1202 Alarm
Hi is there a number associated with this alarm ??
THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
30-03-2010, 09:16 PM #3
Alarm 66 — Electrical Box Thermostat Failure/Reverseencountered, confirm machine configuration.
Rotation (P.28)
NOTE: Alarm 66 is not used or supported. If this condition is
31-03-2010, 05:31 AM #4
31-03-2010, 05:43 AM #5
I don't know if it Helps but the manual I have say's this -
Control box poorly ventilatedor poor electrical connection
Good Luck Grizzly
31-03-2010, 05:59 AM #6
have you checked the phasing on the incoming power to see if it has changed from the original configuration?
31-03-2010, 02:40 PM #7
As in the last post, check your phases and also that another unit is not been fed from the same power supply causing a voltage imbalanced.
We had the same problem where on start-up; the customer was using a generator to give a temporary power supply to the chiller. In the building if the elevator motor turned on it would cause a slight drop in power and the chiller would trip on the same alarm.
31-03-2010, 03:24 PM #8
hello
had same problem recently and its the built in flow switch check flows
aww
31-03-2010, 03:24 PM #9
when the flow switch failure shows a lack of coolant flow
01-04-2010, 07:01 AM #10
19-04-2010, 07:16 PM #11
this is a flow switch fault,check your water flow
20-04-2010, 02:43 PM #12
12-01-2011, 03:41 PM #13
hi im raj i have problem 30gx267 chiller. power off the through control switch for maintanace.then 4days after i turn on control switch i getting alaram 31 and 19 scpm board not responding what is the reason any body help me?scpm board led red light blinking and green light not blinking
12-01-2011, 07:13 PM #14
07 30 Circuit A Reclaim Pumpdown
Pressure Transducer
Measured voltage is
0 vdc or SST > EWT and
EXV < 50% for 1 minute
None Automatic Configuration error
08 31 Circuit B Reclaim Pumpdown
Pressure Transducer
12-01-2011, 07:14 PM #15
21 19 Space Temperature
Thermistor
Temperature measured
by the controller is
outside of the range
of –40 F to 245 F
Alarm tripped Automatic Faulty Sensor, wiring
error, failed EMM
board
Dunham Bush Chiller Alarm
By Regulator in forum Air ConditioningReplies: 11Last Post: 08-12-2010, 01:42 AM -
Carrier chiller basic board problem
By noushad123 in forum Trouble ShootingReplies: 25Last Post: 17-06-2010, 06:55 AM -
Carrier Chiller Help
By superswill in forum Trouble ShootingReplies: 7Last Post: 18-01-2007, 10:06 PM -
Carrier chiller oil migration
By lowtech in forum IndustrialReplies: 5Last Post: 30-04-2006, 04:11 PM