    hi, can anybody explain me that what type of oil lubrication is present in screw compressor, because i have didnt seen any oil pressure cutout, oil pressure readings, high or low oil pressure. BSE 170 oil is used in this compressor. how to check the oil pressure and what type of lubrication is installed in this type of compressor?



  2. #2
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: Bitzer screw compressor csh8551-110y-35p

    hi these bitzer screws have sight glass and you can see oil level, and the oil pressure is suction pressure minus the discharge pressure, they also have oil temp sensor which is linked with the thermistor control module and discharge pipe temp sensor. they have built on oil seperator which seperates the oil from discharge gas, and the oil is pushed round the oil galleries ,lubricating the moving components,with discharge gas pressure, they are very good compressors with preloaded bearings

  3. #3
    Join Date
    Jul 2009
    Location
    Brisbane
    Age
    67
    Posts
    79
    Rep Power
    15

    Re: Bitzer screw compressor csh8551-110y-35p

    Sadiq, The above explanation pretty well covers it. The reason there is no oil pressure differential control is due to the compressor not having an oil pump to create oil pressure, therefore no control is needed as there is no oil pump to monitor.

  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Bitzer screw compressor csh8551-110y-35p

    There is also an oil flow switch in the main oil lube line ,which is probably one of the most critical to ensure enough oil is going into the compressor .
    Usually 15 seconds delay on start up and 3 seconds delay after that .
    Other safeties for oil can include float in oil seperator for low oil level .
    Oil temp control for oil into compressor which can be oil cooler bypass / mixing valve to prevent oil dilution ( AMOT valve or similar ) .

  5. #5
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Bitzer screw compressor csh8551-110y-35p

    Hi, sadiq

    Quote Originally Posted by sadiq View Post
    hi, can anybody explain me that what type of oil lubrication is present in screw compressor, because i have didnt seen any oil pressure cutout, oil pressure readings, high or low oil pressure. BSE 170 oil is used in this compressor. how to check the oil pressure and what type of lubrication is installed in this type of compressor?
    please check this link and you can find a lot about Bitzer compressors ..


    http://www.bitzer.de/eng/products/docu/doc_det/15


    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

Similar Threads

  1. Types of oil lubrication in bitzer screw comp
    By sadiq in forum Industrial Compressors
    Replies: 1
    Last Post: 27-03-2010, 10:42 PM
  2. Compressors - screw or reciprocating?
    By Josip in forum Industrial Compressors
    Replies: 18
    Last Post: 27-01-2009, 10:36 PM
  3. Bitzer Screw Compressors
    By Davezz in forum Industrial Compressors
    Replies: 9
    Last Post: 09-02-2008, 09:32 PM
  4. bitzer screw compressor
    By joe magee in forum Supermarket Refrigeration
    Replies: 5
    Last Post: 14-01-2007, 01:30 AM
  5. bitzer screw compressor
    By Tejbir Singh in forum Industrial Compressors
    Replies: 3
    Last Post: 18-08-2006, 06:12 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •