    Have been on a walk-in cooler which have a semi-hermetic compressor Dorin.I need to open system but there is no record of which refrigerant in used.How can I dteremine which.It is around 2 years old.OIl of compressor is POE . What can it be R404A , R134 A ??
    Is there a method on how to check ? The only details found are FRIGO SYSTEM OF30/06



  2. #2
    bpjack's Avatar
    bpjack Guest

    Re: how to identify which refrigerant

    I would get the compressor model number. Check with the manufacturer and it will be rated for either 404A or 134A. (Usually)

    Then, after I opened the system and performed my repair, I would put a fresh charge of gas in. The other possibility is if you can see the tX valve - some of them have the type of refrigerant printed on them.

    I would put in a fresh charge of gas as there are several possible refrigerants that could be in the unit. ie: 134A, 409a, ..etc that will all run in a 134A compressor. If you do not know who worked on the unit, any of them could be in it. Vacuum the system and start with a new charge is the best way to be certain.

  3. #3
    Join Date
    Feb 2005
    Location
    sliema
    Age
    52
    Posts
    138
    Rep Power
    20

    Re: how to identify which refrigerant

    BpJack,
    I need to replace two flexible pipes that connect one to the high side and high pressure switcha and the other for the low side,they are cracked,so maybe there is no need to loose a lot of refrigerant.The model of the compressor is Dorin K750CC-02(HFC).Any idea.

  4. #4
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: how to identify which refrigerant

    Quote Originally Posted by kerrcell View Post
    HI Guys,
    Have been on a walk-in cooler which have a semi-hermetic compressor Dorin.I need to open system but there is no record of which refrigerant in used.How can I dteremine which.It is around 2 years old.OIl of compressor is POE . What can it be R404A , R134 A ??
    Is there a method on how to check ? The only details found are FRIGO SYSTEM OF30/06

    Fit your gauges shut it down let it equalize then take your p/t chart compare the readings to ambient temp
    My wife used to say you never listen to a word I say at least I think that what she said

  5. #5
    Join Date
    Feb 2005
    Location
    sliema
    Age
    52
    Posts
    138
    Rep Power
    20

    Re: how to identify which refrigerant

    Will try it out toosh thanks

  6. #6
    Join Date
    Feb 2010
    Location
    England
    Age
    60
    Posts
    242
    Rep Power
    16

    Re: how to identify which refrigerant

    .
    Why not just look at the lable on the TEV?

    coolrunnings

    .

  7. #7
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: how to identify which refrigerant

    You can also check the high pressure control, if 404 is used it will be set for about 250psi and 134 would be set for about 180psi.

  8. #8
    Join Date
    Aug 2006
    Location
    Spencer ma.
    Age
    60
    Posts
    108
    Rep Power
    18

    Re: how to identify which refrigerant

    In today's world any one w/ a set of gauges is doing this and will put what they have in a system.
    If you are wondering what is in it! The only true test is a p/t chart and gauges @ ambient temp.
    Checking the high pressure control will only put you in the ball park. Checking the txv is good but takes longer and hope the last guy did not mix the gas pules with this info you now know that they is or is not any air in the system.

  9. #9
    Join Date
    Sep 2007
    Location
    United States
    Posts
    167
    Rep Power
    17

    Re: how to identify which refrigerant

    You can try looking for the condenser plate tag itself. Again these are all " maybe it's this or that " answers. Better to evacuate the system, purge it with nitrogen, change the dryer and sight glass and recharge it with OEM specs. Mark it inside the disconnect box and on the dryer itself with a date. Better to be safe than sorry. Too many " ****tails " from earlier service top-offs. Good luck !! By the way, there are testers available to identify ***** in the field but have heard..some work some don't. Think I'd wait until they get it right.
    Don't leave it like you found it.....Leave it like it should be !!!

  10. #10
    Join Date
    Feb 2005
    Location
    sliema
    Age
    52
    Posts
    138
    Rep Power
    20

    Re: how to identify which refrigerant

    Ok guys,best thing I think is to check on the expansion valve top.The system is new,2 years old and there was never a need to open system.Thanks to all.

  11. #11
    Join Date
    Mar 2010
    Location
    pakistan
    Posts
    44
    Rep Power
    0

    Re: how to identify which refrigerant

    kerrcell
    from the up side of TXV you can see which refregrent is charge in the systme. there code will be print on the top of TXV


  12. #12
    Join Date
    Feb 2005
    Location
    sliema
    Age
    52
    Posts
    138
    Rep Power
    20

    Re: how to identify which refrigerant

    HI Guys,
    Thanks all,found that it runs on R404A.I found on txv,thanks again.

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Leak Testing?
    By Thana in forum Trouble Shooting
    Replies: 36
    Last Post: 31-08-2010, 02:57 PM
  3. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 12:39 PM
  4. MHI FDCA400HKXRE4 Tech Info Please
    By L.JT in forum Trouble Shooting
    Replies: 5
    Last Post: 23-08-2008, 11:00 PM
  5. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •