28-03-2010, 03:07 PM #1
CityMulti on BACnet
I do have 3 black BACnet boxes on CityMulti. No G50 or GA150. Everything on X-cite IQ3; 963 supervisor. So, I can't get fault codes.
Question: how to collect fault codes from Mitsu BACnet controller on Air Con side?
Any free software, or for reasonable price?
/I can't open outdoors, and here ne PAR-21/.
Thank You
P.S.: I haven't design system, client cut on GA150
-
05-04-2010, 09:17 PM #2
Re: CityMulti on BACnet
As far as I know, fault codes are not "passed on" through the a BACnet gateway, can you nott connect a par27 or Monitor Tool PC somewhere on the system? If you cannot "open outdoors" how will you repair the fault if it is an outdoor unit problem?