    Refrigerant piping design



    I recently completed an installation of a Liebert unit for a data room. This system consisted of a roof mounted condenser and the air handler section, w/compressor one floor below. The Liebert installation manual requires an inverted trap on both the discharge and the liquid line. I have read in other souces that the trap in the liquid line is not necessary. My understanding is that it prevents liquid from siphoning out of the condenser, and that it prevents liquid from migrating back to the condenser during the off cycle. It would seem to kepp any aditional weight from liquid refrigerant off the L.L. solenoid or the TXV for units without a solenoid. Any input would be appreciated



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Refrigerant piping design

    My understanding is that it prevents liquid from siphoning out of the condenser, and that it prevents liquid from migrating back to the condenser during the off cycle.
    Do as said in instalation manual.
    If there is no solenoid valve at liquid line it is possible that all liquid migrate from condenser to evaporator during off period (TXV is never 100% closed) and when compressor start, high risk of liquid in compressor is possible.
    Last edited by nike123; 28-03-2010 at 03:07 PM.

  3. #3
    Join Date
    Jun 2008
    Location
    USA
    Age
    55
    Posts
    7
    Rep Power
    0

    Re: Refrigerant piping design

    I definately followed the installation manual. I just want to make sure I have a correct understanding of why this is required.

  4. #4
    Join Date
    Jun 2008
    Location
    USA
    Age
    55
    Posts
    7
    Rep Power
    0

    Re: Refrigerant piping design

    I tried to attach the installation manual, for some reason I couldn't make that happen. It does require inverted traps. It looks like they replaced the L.L.trap in your drawing with a check valve? I don't mean to sound like a dope, I'm fairly new to the trade. I've been an electrician for 23 years. I'm what you might call a re-tread!

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Refrigerant piping design

    Quote Originally Posted by Shatner View Post
    I tried to attach the installation manual, for some reason I couldn't make that happen. It does require inverted traps. It looks like they replaced the L.L.trap in your drawing with a check valve? I don't mean to sound like a dope, I'm fairly new to the trade. I've been an electrician for 23 years. I'm what you might call a re-tread!
    Inverted trap or check valve, they have same function to prevent liquid refrigerant to migrate in off period.

  6. #6
    Join Date
    Jun 2008
    Location
    USA
    Age
    55
    Posts
    7
    Rep Power
    0

    Re: Refrigerant piping design

    Thanks very much

Similar Threads

  1. Best Refrigerant for New Design
    By Andreas11 in forum Refrigerants
    Replies: 9
    Last Post: 05-09-2010, 09:30 AM
  2. Replies: 8
    Last Post: 08-01-2009, 01:08 AM
  3. Cable tray for refrigerant Piping
    By harsen in forum Fundamentals
    Replies: 5
    Last Post: 13-02-2007, 02:02 PM
  4. refrigerant for water distiller
    By star882 in forum Refrigerants
    Replies: 0
    Last Post: 16-12-2006, 05:43 PM
  5. Replies: 31
    Last Post: 28-11-2006, 10:32 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •