    Problem with chiller



    We have a trane chiller, its contain two ckt., our main problem is ckt 2 tripped frequently.
    At tripping time
    CKT 1: Eva. Satu. Temp. -0.7C, eva. Satu. Pr. 4.1 Bar, Condenser Sat. Temp. 58.3C, con. sat. Pr. 22.1 Bar.
    CKT 2: Eva. Satu. Temp. -5.8 C, Eva. Satu. Pr. 3.1 Bar, Condenser Sat. Temp. 44.7 C, Con. sat. Pr. 16.1 Bar.
    And the fault showing A Low ref. CK-2, if we clear it then it show I Service demand or A CK1 limiting.
    What will be our steps now...........



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Problem with chiller

    What is CKT?
    Measure superheat and subcooling.
    Measure water in and out temperatures
    Measure air in and out temperatures.
    What is full model #?
    Measure refrigerant line temperatures at compressor discharge (10" from it), condenser inlet, condenser outlet, filter -dryer inlet and outlet, evaporator outlet, compressor inlet (10" from it).
    Than post all that here for each circuit separatly!

    our main problem is ckt 2 tripped frequently
    Tripped on what? High pressure, low pressure, current overload, flow switch, low temp alarm, low voltage protection?
    Last edited by nike123; 28-03-2010 at 10:07 AM.

  3. #3
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Problem with chiller

    CKT 1: Eva. Satu. Temp. -0.7C, eva. Satu. Pr. 4.1 Bar, Condenser Sat. Temp. 58.3C, con. sat. Pr. 22.1 Bar.
    CKT 2: Eva. Satu. Temp. -5.8 C, Eva. Satu. Pr. 3.1 Bar, Condenser Sat. Temp. 44.7 C, Con. sat. Pr. 16.1 Bar.
    And the fault showing A Low ref. CK-2, if we clear it then it show I Service demand or A CK1 limiting.
    What will be our steps now...........[/QUOTE]

    CKT is circuit

    A Low ref. CKT-2 stands for Alarm low refridgerant circuit 2.

    Machine is either R22 or R404a

    give us the machine type and application and we can help u out.
    If it ain't broke, don't fix it!

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Problem with chiller

    Quote Originally Posted by Lowrider View Post
    Machine is either R22 or R404a
    R22 by his readings.

  5. #5
    Join Date
    Mar 2010
    Location
    Bangladesh
    Age
    40
    Posts
    151
    Rep Power
    15

    Re: Problem with chiller

    CKT means Circuit.
    I have no idea how to measure superheat & sub cool may be we haven’t the instrument.

    Water inlet temp. 10 C & Outlet temp.9 C.
    Air inlet temp: 34 C,
    Outlet temp. Of: Evaporator Fan 1: 41 C, Eva. Fan 2: 42 C, Eva. Fan 3: 47.2 C
    (Note: Fan 1&2 with the 2nd circuit I mean with 2nd circuit compressor & Fan 3 with 1st circuit compressor)

    Model: ECGAH 230,
    Total Circuit No. Two: Capacity: (10T+10T) +10T:
    Ref. required Ckt. 1: 13 kg, ckt2: 6kg
    Max working pressure : LP:16 bar; HP: 32 bar
    Evaporator fan No. 03, Speed: 915 t/mn, kW: 1.74 each
    Three Compressors, 2 in 1st circuit and 1 in second circuits

    Ref. Line Temp.(Circuit 1)
    Compressor discharge (10" from it): 86 C
    Condenser inlet: 110 C
    Condenser outlet: 53 C
    Filter -dryer inlet: 50 C
    Filter -dryer Outlet: 48 C
    Evaporator outlet: 16 C
    Compressor inlet (10" from it): 25 C

    Ref. Line Temp.(Circuit 2)
    Compressor discharge (10" from it): 84 C
    Condenser inlet: 93 C
    Condenser outlet: 41 C
    Filter -dryer inlet: 40 C
    Filter -dryer Outlet: 45 C
    Evaporator outlet: 17 C
    Compressor inlet (10" from it): 19 C
    (Note: All the temperature I measured with Infrared Thermometer)
    At running Condition: Circuit 1: Suction Pressure 71 PSI, & Discharge Pressure: 375 PSI
    Circuit 2: Suction Pressure 60 PSI, & Discharge Pressure: 280 PSI

    Refrigerant: R22
    Faults we are finding:
    • A low ref. ck-2 (probable cause as per manual, Evaporator 2 ref. saturated temp. has overtaken the ref. low temp. set point, check expansion valve & ref. load)
    Plz: clear me what does it means.
    • I Service demand
    • A ckt limiting
    • A Com. I/O: 4

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Problem with chiller

    Quote Originally Posted by Bashir01219 View Post
    (Note: All the temperature I measured with Infrared Thermometer)
    Some temperatures does not make sense (compressor discharge cannot be lower than condenser inlet) which indicate that you did not adjusted emissivity on your IR thermometer.
    http://www.omega.com/techref/iredtempmeasur.html

    Wrap all measuring points with black electrician tape and make reading again or better find some decent calibrated contact thermometer.

  7. #7
    Join Date
    Jul 2003
    Location
    caribbean
    Age
    74
    Posts
    8
    Rep Power
    0

    Re: Problem with chiller

    for R22 60 PSI = about 34F or 1.1C
    the condesnor pressures you listed are high but I don't think part of the problem at this time. The manual is telling you that the refrigerant staurated temp for ckt 2 is lower than the low temp cutout set point for circuit 2. You also have too much superheat in ckt 2 which rukes out low load. it sounds like either ckt 2 is low on refrigerant or you have an expansion valve problem. I'm also concerned that the condesor pressures are too high. Are all the condensor fans working/ Is the condesnor dirty or have rotting fins? Are there non-condensables in the condensor coils?

  8. #8
    Join Date
    Mar 2010
    Location
    Bangladesh
    Age
    40
    Posts
    151
    Rep Power
    15

    Re: Problem with chiller

    Now i have some idea how to measure superheat & subcool temperature, but it requires some time.
    Hope all of you will help me..........

  9. #9
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Problem with chiller

    for the service demand and the IO com 4 u need a Trane tech. they are behaind a password that i'm not allowed to give 2 u.

    Shortage of refridgerant is the most likely fault. U should leak search the machine and refill after the repair.
    If it ain't broke, don't fix it!

  10. #10
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: Problem with chiller

    Check the pressure of water entering and leaving the evaporator, the input filter could be dirty, low water flow resulting in lower saturation temperature of the evaporator

  11. #11
    Join Date
    Mar 2010
    Location
    Bangladesh
    Age
    40
    Posts
    151
    Rep Power
    15

    Re: Problem with chiller

    Thanks to all of u, to help me.
    # Same water pressure entering into the other circuit evaporator too, and there is no poblem. Is their any chance of fault with this circuit evaporator? may be its need to clean.
    But their is no provision of cleaning.

  12. #12
    Join Date
    Apr 2010
    Location
    UK
    Posts
    6
    Rep Power
    0

    Re: Problem with chiller

    Ckt 1 limiting is probably due to your leaving water temp being above 15c whereby it will prevent the last compressor from running.

    Ckt 2 is probably low on refrigerant.

    Com 1/04, is a telling you it is looking for an option board, which is probably not even installed, a setting will change the option, but I can't remember which setting on the SMM, sorry

  13. #13
    Join Date
    Mar 2010
    Location
    Bangladesh
    Age
    40
    Posts
    151
    Rep Power
    15

    Re: Problem with chiller

    Thanks for replay,
    Sir, its help me lot.
    Some of the data in the board is not showing, like B02, E09, E10, E11, E12, B06 etc.
    We have no idea how to troubleshooting this problem?

  14. #14
    Grolly's Avatar
    Grolly Guest

    Re: Problem with chiller

    Narkom. Thanks for the SMM pdf

  15. #15
    Join Date
    Mar 2010
    Location
    Bangladesh
    Age
    40
    Posts
    151
    Rep Power
    15

    Re: Problem with chiller

    I need electrical drawing of the total circuit, I did not find it in the SMM manual.
    Please help!
    Last edited by Bashir01219; 25-02-2011 at 04:27 AM. Reason: Improve

Similar Threads

  1. problem with multistack chiller
    By bright in forum Refrigerants
    Replies: 3
    Last Post: 30-10-2010, 10:43 PM
  2. Problem with mcquay chiller
    By texanul in forum Industrial
    Replies: 6
    Last Post: 04-02-2010, 08:51 PM
  3. Problem with centrifugal chiller
    By engalmohannad in forum Commercial
    Replies: 0
    Last Post: 19-04-2009, 10:00 PM
  4. York YK Chiller Problem
    By icebox in forum Refrigeration Books
    Replies: 13
    Last Post: 01-07-2008, 06:05 PM
  5. Chiller tripping Problem
    By bhasadu in forum Trouble Shooting
    Replies: 0
    Last Post: 21-06-2008, 09:12 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •