hi all i have a hair dressers which wants a/c installing the size of the shop reqs 5.5 kw of cooling, the thing is i have a new mitsubishi 7.5 kw unit sitting around which would be a bonus if i could use it, does anyone see a problem or should it be ok to fit it?
27-03-2010, 10:05 PM #2
Re: advice please
If an inverter, then not a problem, if fixed speed, the humidity in the room may increase
27-03-2010, 10:07 PM #3
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: advice please
No if it is inverter. If not, than it could constantly be in OFF-ON loop and compressor and other parts could be damaged, and high humidity will be present in air.
27-03-2010, 10:08 PM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: advice please
I need to learn to type faster!
27-03-2010, 10:15 PM #5
Re: advice please
thanks for the advice it is an inverter hi wall unit i have!!
27-03-2010, 10:21 PM #6
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
28-03-2010, 03:33 PM #7
Re: advice please
hi all,
could someone explain why it would be high humidity, when the unit is on cooling it dehumidifies doesnt it? do you mean the unit will not be working as frequent therefore humidity will rise?
thanks lee
28-03-2010, 04:56 PM #8
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
02-04-2010, 06:07 AM #9
Re: advice please
May be a 5kw room but have you allowed loading for hair driers, people, glass etc. Sounds a reasonable size. Try to fit a LARGE well inclined drain. These hair dressers clog up a unit quick-smart!
09-04-2010, 10:26 PM #10
Re: advice please
I would say it will be fine, you only get the full duty from them with them being in high fan speed so running it at low fan speed will mean its running closer to the actual required cooling anyway. Oh and less noise for the client!
10-04-2010, 02:48 AM #11
Re: advice please
I say fit the 7.5 kw kit..
hair style shops will produce a high amount of humidity which will greatly increase the amount of kw needed for the room..
since it is an inverter it will vary capacity as needed.. just be sure to locate the high wall where it wont make the patrons uncomfortable.. ice cold air blowing down on wet hair does not make for a very nice time... it gets rather chilled...
-Christopher
10-04-2010, 02:49 AM #12
Re: advice please
Get a free hair cut first. Then you can scan the operation, hair driers, washing stuff, spray gel stuff everywhere, so requires lots of fresh air, that perm cra# has got to be unfriendly. High humidity.
So go with what you have got and pressurized with lots of fresh airLast edited by Magoo; 10-04-2010 at 02:53 AM.
10-04-2010, 03:03 AM #13
Re: advice please
hair spray sucked into the intake of a high wall.. that sounds like nice and sticky for hair to get stuck.. be sure the filters are fitted and tidy
-Christopher
11-04-2010, 11:34 AM #14
Power supply
Also: Not so much a problem with inverters but, with their high electrical consumption, a hairdressers often has an issue with available power at the consumer unit.
ie, it is not just a case of, is there a spare way in the board? but how much spare power do they still have available for the aircon.
11-04-2010, 09:56 PM #15
Re: advice please
We look after a hairdressers! Your gona need loads of coil cleaner come service time! Hairspray is a bloody nightmare!
Techinical advice on Fujitsu AOT30RMAL?
By Taaz1275 in forum Technical DiscussionsReplies: 15Last Post: 24-06-2011, 03:35 AM -
career advice needed
By carfy313 in forum TrainingReplies: 4Last Post: 28-03-2010, 09:17 AM -
Getting Colder, need advice
By mvtop in forum FundamentalsReplies: 54Last Post: 29-11-2009, 01:49 AM -
Seeking Advice on Retraining for AC&R
By Stu76 in forum TrainingReplies: 5Last Post: 23-08-2008, 10:52 AM -
Career advice please.
By james 100 in forum Chit Chat & Service StoriesReplies: 14Last Post: 13-09-2007, 06:37 PM