    advice please



    hi all i have a hair dressers which wants a/c installing the size of the shop reqs 5.5 kw of cooling, the thing is i have a new mitsubishi 7.5 kw unit sitting around which would be a bonus if i could use it, does anyone see a problem or should it be ok to fit it?



  2. #2
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: advice please

    If an inverter, then not a problem, if fixed speed, the humidity in the room may increase

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: advice please

    No if it is inverter. If not, than it could constantly be in OFF-ON loop and compressor and other parts could be damaged, and high humidity will be present in air.

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: advice please

    I need to learn to type faster!

  5. #5
    Join Date
    May 2007
    Location
    scotland
    Posts
    756
    Rep Power
    19

    Re: advice please

    thanks for the advice it is an inverter hi wall unit i have!!

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: advice please

    Quote Originally Posted by coolhibby1875 View Post
    thanks for the advice it is an inverter hi wall unit i have!!
    Keep in mind that single compressor inverter cannot ramp down below 30% capacity!

  7. #7
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: advice please

    hi all,

    could someone explain why it would be high humidity, when the unit is on cooling it dehumidifies doesnt it? do you mean the unit will not be working as frequent therefore humidity will rise?

    thanks lee

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: advice please

    Quote Originally Posted by moondawn View Post
    hi all,

    could someone explain why it would be high humidity, when the unit is on cooling it dehumidifies doesnt it? do you mean the unit will not be working as frequent therefore humidity will rise?

    thanks lee
    If your unit works 70% OFF and 30% ON than dehumidifier is much lower than when this ratio is in reversal.

  9. #9
    Join Date
    Aug 2009
    Location
    Australia
    Posts
    10
    Rep Power
    0

    Re: advice please

    May be a 5kw room but have you allowed loading for hair driers, people, glass etc. Sounds a reasonable size. Try to fit a LARGE well inclined drain. These hair dressers clog up a unit quick-smart!

  10. #10
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: advice please

    I would say it will be fine, you only get the full duty from them with them being in high fan speed so running it at low fan speed will mean its running closer to the actual required cooling anyway. Oh and less noise for the client!

  11. #11
    Join Date
    Jun 2009
    Location
    Columbus Ohio
    Age
    55
    Posts
    169
    Rep Power
    15

    Re: advice please

    I say fit the 7.5 kw kit..

    hair style shops will produce a high amount of humidity which will greatly increase the amount of kw needed for the room..

    since it is an inverter it will vary capacity as needed.. just be sure to locate the high wall where it wont make the patrons uncomfortable.. ice cold air blowing down on wet hair does not make for a very nice time... it gets rather chilled...
    -Christopher

  12. #12
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: advice please

    Get a free hair cut first. Then you can scan the operation, hair driers, washing stuff, spray gel stuff everywhere, so requires lots of fresh air, that perm cra# has got to be unfriendly. High humidity.
    So go with what you have got and pressurized with lots of fresh air
    Last edited by Magoo; 10-04-2010 at 02:53 AM.

  13. #13
    Join Date
    Jun 2009
    Location
    Columbus Ohio
    Age
    55
    Posts
    169
    Rep Power
    15

    Re: advice please

    hair spray sucked into the intake of a high wall.. that sounds like nice and sticky for hair to get stuck.. be sure the filters are fitted and tidy
    -Christopher

  14. #14
    Join Date
    May 2006
    Location
    Sussex
    Posts
    362
    Rep Power
    21

    Power supply

    Quote Originally Posted by Steve J C View Post
    May be a 5kw room but have you allowed loading for hair driers, people, glass etc. Sounds like a reasonable size.
    Also: Not so much a problem with inverters but, with their high electrical consumption, a hairdressers often has an issue with available power at the consumer unit.

    ie, it is not just a case of, is there a spare way in the board? but how much spare power do they still have available for the aircon.

  15. #15
    Join Date
    Jun 2009
    Location
    East Anglia
    Age
    38
    Posts
    204
    Rep Power
    15

    Re: advice please

    We look after a hairdressers! Your gona need loads of coil cleaner come service time! Hairspray is a bloody nightmare!

Similar Threads

  1. Techinical advice on Fujitsu AOT30RMAL?
    By Taaz1275 in forum Technical Discussions
    Replies: 15
    Last Post: 24-06-2011, 03:35 AM
  2. career advice needed
    By carfy313 in forum Training
    Replies: 4
    Last Post: 28-03-2010, 09:17 AM
  3. Getting Colder, need advice
    By mvtop in forum Fundamentals
    Replies: 54
    Last Post: 29-11-2009, 01:49 AM
  4. Seeking Advice on Retraining for AC&R
    By Stu76 in forum Training
    Replies: 5
    Last Post: 23-08-2008, 10:52 AM
  5. Career advice please.
    By james 100 in forum Chit Chat & Service Stories
    Replies: 14
    Last Post: 13-09-2007, 06:37 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •