Fujitsu Split System Outdoor Fan Wiring Issue
Hey all, new to these forums and to messing around with split systems. Am qualified refrig mechanic, but only experienced with transport refrigeration (Thermo King, etc).
Anyways...
I have a Fujitsu split system problem, indoor unit turns on okay, and indoor fan runs okay. However, ventured outside... compressor running, but outdoor fan not running. So no surprises to it having no cooling effect. Removed some covers, made sure fan not seized, etc. Noticed @ the 6 terminal motor starter the Neutral wire is very badly damaged and getting hot whilst running. (Burning smell and insulation previously starting to melt)
Just wondering if motor starters are a common problem in a/c units, like if its an internal fault within the starter itself that would cause such a thing or something like the fan motor capacitor?
Looks like its gotten hot only @ Neutral terminal where it clips onto the starter, i was thinking maybe bad connection causing high resistance therefore caused it to heat up, get hot, and cook the starter?
Probably something simple, i havent really had a go at anything to do with split systems before so any advice would be greatly appreciated.
Also, outdoor unit model AOT30R if that helps at all
-
27-03-2010, 12:30 PM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Fujitsu Split System Outdoor Fan Wiring Issue
There are 3 more letters after R at outdoor unit model#!
Measure the curent at that neutral wire. If current is in limits for that wire size you have bad contact!Last edited by nike123; 27-03-2010 at 12:32 PM.
-
27-03-2010, 10:54 PM #3
Re: Fujitsu Split System Outdoor Fan Wiring Issue
Sounds like a poor contact type burn out.
Mechanical failure due to loose terminal, pinch it tight and restart.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
29-03-2010, 03:04 AM #4
Re: Fujitsu Split System Outdoor Fan Wiring Issue
Yeah you can get burnt terminals on the soft starter due to wiring getting loose.
But that only affects the compressor, the fan is completely different circuit and not wired through the soft starter.
Either open circuit fan motor or capacitor, or indoor relay/wiring problem.
Similar Threads
-
Daikin fault codes
By Chris2005 in forum Air ConditioningReplies: 45Last Post: 21-03-2012, 10:09 PM -
LG split system fan cont. trouble shooting
By ianv in forum Trouble ShootingReplies: 9Last Post: 01-02-2011, 03:31 PM -
E3 error message Fujita split system air con
By espiby in forum Air ConditioningReplies: 1Last Post: 07-11-2009, 10:12 AM -
fujitsu multi split, how it works??
By 123-steve909 in forum Air ConditioningReplies: 9Last Post: 04-06-2009, 07:07 AM -
Split type wall mounting Air Conditioning system
By stevews in forum Air ConditioningReplies: 23Last Post: 11-07-2005, 09:55 AM