    Fujitsu Split System Outdoor Fan Wiring Issue


    Hey all, new to these forums and to messing around with split systems. Am qualified refrig mechanic, but only experienced with transport refrigeration (Thermo King, etc).
    Anyways...
    I have a Fujitsu split system problem, indoor unit turns on okay, and indoor fan runs okay. However, ventured outside... compressor running, but outdoor fan not running. So no surprises to it having no cooling effect. Removed some covers, made sure fan not seized, etc. Noticed @ the 6 terminal motor starter the Neutral wire is very badly damaged and getting hot whilst running. (Burning smell and insulation previously starting to melt)

    Just wondering if motor starters are a common problem in a/c units, like if its an internal fault within the starter itself that would cause such a thing or something like the fan motor capacitor?

    Looks like its gotten hot only @ Neutral terminal where it clips onto the starter, i was thinking maybe bad connection causing high resistance therefore caused it to heat up, get hot, and cook the starter?

    Probably something simple, i havent really had a go at anything to do with split systems before so any advice would be greatly appreciated.

    Also, outdoor unit model AOT30R if that helps at all



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    48
    Posts
    5,951
    Blog Entries
    5
    Rep Power
    22

    Re: Fujitsu Split System Outdoor Fan Wiring Issue

    There are 3 more letters after R at outdoor unit model#!
    Measure the curent at that neutral wire. If current is in limits for that wire size you have bad contact!
    Last edited by nike123; 27-03-2010 at 01:32 PM.
    Now, when I am officialy citizen off EU, I am looking for decent job! For any job offer please check my profile!

  3. #3
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    66
    Posts
    10,108
    Rep Power
    41

    Re: Fujitsu Split System Outdoor Fan Wiring Issue

    Sounds like a poor contact type burn out.

    Mechanical failure due to loose terminal, pinch it tight and restart.
    Brian - Torquay, Devon, UK
    I have to stop saying "how stupid can you be?" to my co-workers.
    They're starting to take it as a challenge...

    BASIC MAINTENANCE. If it doesn't move and it should then use WD40. If it moves but it shouldn't then use Duct Tape.

  4. #4
    Join Date
    Jul 2007
    Location
    Australia
    Age
    40
    Posts
    1,879
    Rep Power
    11

    Re: Fujitsu Split System Outdoor Fan Wiring Issue

    Yeah you can get burnt terminals on the soft starter due to wiring getting loose.
    But that only affects the compressor, the fan is completely different circuit and not wired through the soft starter.
    Either open circuit fan motor or capacitor, or indoor relay/wiring problem.

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 11:09 PM
  2. LG split system fan cont. trouble shooting
    By ianv in forum Trouble Shooting
    Replies: 9
    Last Post: 01-02-2011, 04:31 PM
  3. E3 error message Fujita split system air con
    By espiby in forum Air Conditioning
    Replies: 1
    Last Post: 07-11-2009, 11:12 AM
  4. fujitsu multi split, how it works??
    By 123-steve909 in forum Air Conditioning
    Replies: 9
    Last Post: 04-06-2009, 07:07 AM
  5. Split type wall mounting Air Conditioning system
    By stevews in forum Air Conditioning
    Replies: 23
    Last Post: 11-07-2005, 09:55 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •