    Unhappy Cooler charge confusion



    Hi
    I've recieved 2 small coolers that doesn't cool
    both same brand both brand new.

    1/6th hp compressors, 134-A, 4.6oz, 2.5 amps on the
    sticker inside (but 2.9 amps on their website)
    These were shipped from outside the US that is why
    the owner didn't want to return it. $$$

    So I hook up the manifold nothing... no refrigerant
    I see where the access valve is there is a hole where is bends ...so this unit could have never been tested...

    fix the hole...blew the capillaire to make sure it was not clogged... replace the filter/drier

    Charge to manufacturer specs 4.6oz...not cooling at all...so now I am confused and I am thinking maybe
    my weight scale is playing tricks on me... so I weigh my bottle ....charge the unit again to 4.6oz ...then check weight again...seems correct but still no cooling :/

    so I continue to fill the unit to about 20F and the unit cools now... reaches 44F which is still not satisfactory

    the other cooler has refrigerant in it but doesn't cool
    so I charge it to 20F and it ices up... contacted the manufacturer told us to charge to 25F still ices up
    charged it to about 30F the cooler reaches 48F but will not go any lower...

    anyone have some suggestions to these problems
    anyone have some ideas what the superheat/subcooling would need to be for these small appliances I would like to really know what the problem is with these units

    ambient temp here is about 82F it is any help...

    any help would be apreciated
    Thanks



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Cooler charge confusion

    Give us make and model#!

  3. #3
    Matadem's Avatar
    Matadem Guest

    Re: Cooler charge confusion

    Cooler info
    Ascend
    JGD-06R
    s/n:GC6R-0908-0235
    6 cu ft.

    Thanks

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Cooler charge confusion

    http://www.ascendmfg.com/PDFs/JGD-06R&06R-PT.pdf

    Maybe they fitted incorrect capillaries. What is compressor make and model #.
    Remove charge and fill amount stated at sticker than measure superheat, pressures, inside and outside temperature, discharge line temperature condenser outlet line temperature and filter-dryer temperature and post here.
    Last edited by nike123; 27-03-2010 at 12:25 PM.

  5. #5
    Matadem's Avatar
    Matadem Guest

    Re: Cooler charge confusion

    Compressor info:
    LG NS36HAQG
    1ph 110-115V 60 Hz
    LRA12 134-A
    CP17120091060141

    Charged the unit again at 4.6oz
    after 20min the pressure is stable at
    sp 20psi - 22F
    superheat 73F-22F=51F ???
    Ambient temp 78F
    inside cabinet temp 60F
    Filter/drier temp 99F
    inlet condenser 106F
    outlet condenser 102F
    inlet evap 36F (evap starts freezing)
    outlet evap 73F
    inlet compressor 86F at 2" distance
    outlet compressor 137F at 2" distance
    inlet evap fan suction in cabinet 60F
    out evap fan blows in cabinet 53F

    amps at 2.3A

    This is all the readings that I took.

    Thanks

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Cooler charge confusion

    What are the condenser air in and air out temps?

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Cooler charge confusion

    • LOW CHARGE = High superheat. Low suction pressure, indoor TD, subcooling, head pressure & compressor current draw.
    • MILD RESTRICTION (factory charge) = High superheat. Lowsuction pressure, indoor TD & current draw. Normal to high subcooling. Normal to low head pressure.

    I vote for low charge.

    Add charge by no more than 1-2% of amount already in (critically charged system like your is very sensitive to charge amount).

    Leave unit to work for 20-30 min and check again all readings as before.
    Specially monitor suction line temperature after topping up. When you are near or at correct charge suction line temperature should start dropping very fast. Then it will rise again if you overcharge it.



    If careful topping don't bring much results than your capillary tube is probably too long or too small diameter.

    If you really want to sort it out easy than braze some process tube with access port at high side and monitor high pressure and subcooling. If subcooling is low, you have low charge, if high, you have restriction and refrigerant collecting in condenser.
    Later you could crimp process tube few times and with crimp pliers still pressed at last crimp, cut access port and weld pipe fast with silver.
    Leave at least 10 cm between last two crimps and cool pipe with wet rag during brazing.

    P.S. Take readings of temperature of pipes at least 10" from compressor.
    Last edited by nike123; 28-03-2010 at 09:28 AM.

  8. #8
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Cooler charge confusion

    Quote Originally Posted by nike123 View Post
    • LOW CHARGE = High superheat. Low suction pressure, indoor TD, subcooling, head pressure & compressor current draw.
    • MILD RESTRICTION (factory charge) = High superheat. Lowsuction pressure, indoor TD & current draw. Normal to high subcooling. Normal to low head pressure.

    I
    This holds true only if/when the box is down to design temp, especially on a cap tube system.

    If it is cooling, wait for the temp to come down, then take a new set of temp readings. On an intial pulldown with high humidity, this could take overnight.

Similar Threads

  1. split inverter unsure of proper charge spec.. how to charge?
    By cadillackid in forum Air Conditioning
    Replies: 4
    Last Post: 19-11-2009, 01:52 PM
  2. Gas charge for portable beer cooler?
    By tom the blade in forum Technical Speculations
    Replies: 5
    Last Post: 11-09-2009, 09:07 AM
  3. Fabrication of Cooler Tube & Shell Cooler
    By rickyccong in forum Technical Discussions
    Replies: 1
    Last Post: 27-07-2009, 02:25 PM
  4. To charge or not to charge?
    By Fire and Ice in forum Old Refrigeration Photos
    Replies: 12
    Last Post: 20-01-2008, 08:11 PM
  5. Who's in charge?
    By chillin out in forum Chit Chat & Service Stories
    Replies: 1
    Last Post: 01-10-2006, 10:51 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •