    Frosting Evap



    Hi guys, can someone explain to me, scientifically, why when a system is low on refrigerant, the evaporator can ifrost up. For example an r22 DX coil on an AHU with full fresh air. thanks



  2. #2
    Join Date
    Feb 2010
    Location
    England
    Age
    60
    Posts
    242
    Rep Power
    16

    Re: Frosting Evap

    Quote Originally Posted by Collie View Post
    Hi guys, can someone explain to me, scientifically, why when a system is low on refrigerant, the evaporator can ifrost up. For example an r22 DX coil on an AHU with full fresh air. thanks

    It is simple realy.

    Refrigerants are temperature / pressure related.

    If you lower the pressure you lower the temp at which the refrigerant boils.

    So if your system is short of gas, the expansion valve opens fully because the the superheat at the exit of the evap is too high. Because the system is short of gas the pressure inside the evap is lower than it would normaly be.
    This lower pressure results in a lower temp at the first part of the evap and it causes the water too freeze and then that causes a reduced air flow over the evap which then compounds the problem and the evap runs even colder.

    coolrunnings

    .

  3. #3
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    48
    Posts
    412
    Rep Power
    22

    Re: Frosting Evap

    Even if any refrigerant, If evaporator temperature is going to below 32F or 0c, it will make ice on coil. So all refrigerant should boil at a temperature of 4.4c (40F) inside the evaporator (for high temp.applications). To achieve this in evaporator should maintain proper refrigerant pressure related to its temperature.

    Moideen-dubai

  4. #4
    Join Date
    Aug 2009
    Location
    utah
    Posts
    83
    Rep Power
    15

    Re: Frosting Evap

    Quote Originally Posted by moideen View Post
    Even if any refrigerant, If evaporator temperature is going to below 32F or 0c, it will make ice on coil. So all refrigerant should boil at a temperature of 4.4c (40F) inside the evaporator (for high temp.applications). To achieve this in evaporator should maintain proper refrigerant pressure related to its temperature.

    Moideen-dubai
    True. But I like 45/80 pressure/temp relation..

Similar Threads

  1. Evap losing capacity
    By chillyblue in forum Trouble Shooting
    Replies: 13
    Last Post: 02-10-2007, 10:04 PM
  2. iced up evap coil
    By wilks in forum Fundamentals
    Replies: 6
    Last Post: 31-08-2007, 09:15 PM
  3. Quest sandwich cooler evap?
    By The MG Pony in forum Commercial
    Replies: 6
    Last Post: 31-05-2007, 07:58 PM
  4. Replies: 10
    Last Post: 21-01-2007, 01:08 AM
  5. Evap motor no come on
    By Apprentice in forum Technical Discussions
    Replies: 13
    Last Post: 04-12-2003, 04:07 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •