    Chilled water pressure



    Hi guys i went into a plant room to look at a compressor and i saw the water pressure gauge and it was reading about 110 psi, and i asked the engineer if the guage was correct and was told yes . i have never come across more than 4 bar water pressure, has anybody else seen this sort of pressure on a water chiller.



  2. #2
    Join Date
    Oct 2007
    Location
    Britain
    Posts
    220
    Rep Power
    17

    Re: Chilled water pressure

    Hi Ghaz,

    Not personally, what was the application, was it process cooling for some sort of machinery?

    Cheers
    Tutto il Mondo e un Paese

  3. #3
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: Chilled water pressure

    It was aircon for offices

  4. #4
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Chilled water pressure

    How tall was the system (building height)?

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Chilled water pressure

    It takes 12psi to push a column of water up 28ft. It takes 120psi for a 280ft high system.

    If this minimum pressure is not maintained, there will be a vacuum at the top causing all sorts of air lock problems.

    Being non-scientific, I just figure out the height of the building and divide by 2. This gives me a little extra.

  6. #6
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Chilled water pressure

    Quote Originally Posted by Gary View Post
    It takes 12psi to push a column of water up 28ft. It takes 120psi for a 280ft high system.

    If this minimum pressure is not maintained, there will be a vacuum at the top causing all sorts of air lock problems.

    Being non-scientific, I just figure out the height of the building and divide by 2. This gives me a little extra.
    Thanks Gary
    That is a useful tip!
    Grizzly

  7. #7
    Join Date
    Mar 2010
    Location
    Dammam
    Posts
    83
    Rep Power
    15

    Re: Chilled water pressure

    Indeed having a 110 psi chilled water supply pressure is too high based on my experience in plant aircon chillers. What is the TDH requirement of your chilled water pipeline loop?,or better yet check the chilled water return pressure or the suction pressure of the chilled pump near the chiller,the pressure should be in the range of 20-25 psi to be able to have good chilled water recirculation as well as minimize pipeline leaks brought about by high pressure within the pipe loop.

  8. #8
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: Chilled water pressure

    Hi GHAZ
    Gary is right. I must assume the pressure was at the bottom of the building. You can get high pressure chillers for locating at the bottom of a building but they are not common.

  9. #9
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: Chilled water pressure

    hi its a 4 storey high building and the water pumps are in the basement

  10. #10
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: Chilled water pressure

    Thanks GHAZ
    That pressure doesn't sound out of the ordinary. Other considerations would be on a cooler day most of the chilled water valves would be shut, if installed the chilled water bypass valve may not be callibrated correctly to maintain the required system pressure differential, and most chillers would have around 20 to 60 psi press drop through the coooer, or the pump coud be oversized and the butterfly valve could be backed off to minimise cavitation.

Similar Threads

  1. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Replies: 9
    Last Post: 10-03-2009, 01:03 PM
  2. Chilled water binder test point
    By Thermatech in forum Tools and Calculators
    Replies: 14
    Last Post: 12-11-2008, 06:30 PM
  3. Chilled water bypass problem
    By MACT in forum Trouble Shooting
    Replies: 5
    Last Post: 16-10-2008, 02:01 AM
  4. Chilled water treatment
    By benj in forum Commercial
    Replies: 1
    Last Post: 04-09-2007, 04:44 AM
  5. chilled water PHE
    By priti in forum Trouble Shooting
    Replies: 1
    Last Post: 31-07-2002, 08:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •