lubricant temperature at suction pipe
Hi,everyone!
As in the suction piper, there are liquid and gas refrigerant, also there are lubricant. Which temperature is higher? Lubricant or refrigerant gas?
I think gas has a higer temperature because gas are superheated while lubricant oil has liquid refrigerant which may at the saturation temperature?
What do you think? And do you have any information about this? Any thesis, paper?
Thanks!
-
26-03-2010, 04:05 AM #2
Re: lubricant temperature at suction pipe
If it is the suction line, there should be no liquid, all should be superheated to some level, oil is transported as a mist (excludes the slug from a suction riser), so does does not carry liquid, suspended in the vapour.
If liquid and vapour are present in the same place (flowing pipe, then all will be at saturation, same temperature)
-
26-03-2010, 05:19 AM #3
Re: lubricant temperature at suction pipe
There are possiblity that liquid exist in suction pipe.
Regardless if there is luquid or not, what is the lubricant temperature, higher or lower that refirgerant gas?
-
26-03-2010, 07:31 AM #4
Re: lubricant temperature at suction pipe
Stiil waiting online for your reply!
-
26-03-2010, 08:50 AM #5
-
26-03-2010, 10:38 AM #6
Re: lubricant temperature at suction pipe
Very Sorry, Mad fridgie! My fault that made you think I am very rude. But I didn't meant it. Hope you will forgive me.
Do you have any material about this?
-
26-03-2010, 10:41 AM #7
Re: lubricant temperature at suction pipe
And Mad fridgie, do you think there is liquid oil on the inner face of the pipe?
Will the oil on the inner face influence the temperature of the pipe.
Coz I am consider whether I will place the TXV bulb on the vertical pipe.
-
26-03-2010, 12:15 PM #8
Re: lubricant temperature at suction pipe
Interesting question, I agree that the oil would be at saturation temperature whilst the refrigerant should be above/superheated.
Yes the oil will affect the pipe temperature and phial location if on a horizontal pipe should reflect this.
CheersTutto il Mondo e un Paese
Similar Threads
-
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
Copeland select 6
By Copman in forum Tools and CalculatorsReplies: 9Last Post: 27-05-2010, 09:01 PM -
Some information on the aplication of suction gas/liquid line heat exchangers
By SteinarN in forum FundamentalsReplies: 5Last Post: 14-09-2009, 07:33 AM -
Measurement of pipe lengths
By batfink in forum Technical DiscussionsReplies: 11Last Post: 23-09-2008, 09:50 PM -
TK basic micro-p features and functions
By REEFER-TEK in forum TransportReplies: 0Last Post: 05-12-2007, 06:25 PM