    Insulated pipe condensations



    Hi every body
    We are doing some refrigerant replacing, including pipe change and insulation replacing too.

    The original refrigerant is R22, and we are designing instalations to use R507. But we are having problems because suction line has condensations.

    In different installations, we have changed between insulation's tickness and brand, but the problem is the same.

    Evaporating temperatures are -35 / -40 ºC (-31/-40 F). Insulation brand is Armacell / Armaflex and Insulation tickness are 19 or 40 mm (3/4" - 1 1/2" approx)

    Does any one know which is the reason of this problem, and any probable solution?

    Thanks a lot.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Insulated pipe condensations

    Has the insulation been properly installed to ensure good vapour sealing?

    Is the condensation inside the insulation or outside?

    Have you used cable ties to fix the pipework and pinched the insulation?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Aug 2006
    Location
    BCN, Spain
    Age
    43
    Posts
    6
    Rep Power
    0

    Re: Insulated pipe condensations

    Hi Brian
    Thanks for your help...

    The insulation has been properly installed. There in no discontinuity on insulation surface.

    The condensation is outside of the insulation wall.

    We don't use to use cable ties to fix pipes. We allways use isofonic suports outside or inside of the insulation material, already properly isolated.

    The problem is that we can see water outside the insulation pipe.

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Insulated pipe condensations

    Quote Originally Posted by refrigeracioncr View Post
    The insulation has been properly installed. There in no discontinuity on insulation surface.

    The condensation is outside of the insulation wall.



    The problem is that we can see water outside the insulation pipe.
    Condensation outside mean that insulation thickness is insufficient for insulation surrounding air temperature and humidity and that surface temperature of insulation is below dew point of surrounding air.

    What is max humidity and temperature of surrounding air?

    Check here your required insulation thickness for your conditions (pipe temperature, air temperature, humidity, pipe dia).
    Last edited by nike123; 26-03-2010 at 07:47 AM.

  5. #5
    Join Date
    Aug 2006
    Location
    BCN, Spain
    Age
    43
    Posts
    6
    Rep Power
    0

    Re: Insulated pipe condensations

    Hi Nike
    Thanks a lot for the link.
    We will use it to calculate the adecuated insulation tickness and correct it to solve the problem.
    I had made some calculations and its very probably that thickness is too thin.

Similar Threads

  1. Chilled water pipe sizing?
    By monkey spanners in forum Technical Speculations
    Replies: 4
    Last Post: 07-08-2009, 04:31 PM
  2. Burst Pipe caused by Abrasion. (aka Only on a Friday)
    By Grizzly in forum Chit Chat & Service Stories
    Replies: 11
    Last Post: 19-09-2008, 06:59 PM
  3. Pre insulated Pipe work
    By gwilliamson in forum Air Conditioning
    Replies: 4
    Last Post: 11-07-2008, 11:36 AM
  4. Mitsubishi PUHZ-RP200YHA Pipe Sizes
    By gwilliamson in forum Air Conditioning
    Replies: 11
    Last Post: 14-05-2008, 09:43 PM
  5. Pipe sizes
    By benncool in forum Chit Chat & Service Stories
    Replies: 10
    Last Post: 08-07-2003, 10:58 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •