25-03-2010, 01:04 PM #1
Insulated pipe condensations
Hi every body
We are doing some refrigerant replacing, including pipe change and insulation replacing too.
The original refrigerant is R22, and we are designing instalations to use R507. But we are having problems because suction line has condensations.
In different installations, we have changed between insulation's tickness and brand, but the problem is the same.
Evaporating temperatures are -35 / -40 ºC (-31/-40 F). Insulation brand is Armacell / Armaflex and Insulation tickness are 19 or 40 mm (3/4" - 1 1/2" approx)
Does any one know which is the reason of this problem, and any probable solution?
Thanks a lot.
-
25-03-2010, 07:05 PM #2
Re: Insulated pipe condensations
Has the insulation been properly installed to ensure good vapour sealing?
Is the condensation inside the insulation or outside?
Have you used cable ties to fix the pipework and pinched the insulation?Brian - Newton Abbot, Devon, UK
Retired March 2015
-
26-03-2010, 07:01 AM #3
Re: Insulated pipe condensations
Hi Brian
Thanks for your help...
The insulation has been properly installed. There in no discontinuity on insulation surface.
The condensation is outside of the insulation wall.
We don't use to use cable ties to fix pipes. We allways use isofonic suports outside or inside of the insulation material, already properly isolated.
The problem is that we can see water outside the insulation pipe.
-
26-03-2010, 07:36 AM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Insulated pipe condensations
Condensation outside mean that insulation thickness is insufficient for insulation surrounding air temperature and humidity and that surface temperature of insulation is below dew point of surrounding air.
What is max humidity and temperature of surrounding air?
Check here your required insulation thickness for your conditions (pipe temperature, air temperature, humidity, pipe dia).Last edited by nike123; 26-03-2010 at 07:47 AM.
-
29-03-2010, 10:24 AM #5
Re: Insulated pipe condensations
Hi Nike
Thanks a lot for the link.
We will use it to calculate the adecuated insulation tickness and correct it to solve the problem.
I had made some calculations and its very probably that thickness is too thin.
Similar Threads
-
Chilled water pipe sizing?
By monkey spanners in forum Technical SpeculationsReplies: 4Last Post: 07-08-2009, 04:31 PM -
Burst Pipe caused by Abrasion. (aka Only on a Friday)
By Grizzly in forum Chit Chat & Service StoriesReplies: 11Last Post: 19-09-2008, 06:59 PM -
Pre insulated Pipe work
By gwilliamson in forum Air ConditioningReplies: 4Last Post: 11-07-2008, 11:36 AM -
Mitsubishi PUHZ-RP200YHA Pipe Sizes
By gwilliamson in forum Air ConditioningReplies: 11Last Post: 14-05-2008, 09:43 PM -
Pipe sizes
By benncool in forum Chit Chat & Service StoriesReplies: 10Last Post: 08-07-2003, 10:58 PM