    Trane Chiller Problem



    Dear Sir,

    We have an old Traine Chiller Model: ECGAH230, But didn’t have any documents like manual/or others.
    Plz help us.
    Local Supplier is unable to help us.


    With thanks and kind regards,



    Sk. Bashir Abdullah



  2. #2
    Join Date
    Mar 2010
    Location
    Bangladesh
    Age
    40
    Posts
    151
    Rep Power
    15

    Re: Trane Chiller Problem

    Thanks.
    I am looking for CGAH madel not CXAN madel.

  3. #3
    fahed's Avatar
    fahed Guest

    Re: Trane Chiller Problem

    hi ;

    please search this (C10 IM 002 E - 0599) in google
    I think you find what you want .

  4. #4
    Join Date
    Mar 2010
    Location
    Bangladesh
    Age
    40
    Posts
    151
    Rep Power
    15

    Re: Trane Chiller Problem

    Sorry, i didnt got that!

  5. #5
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: Trane Chiller Problem

    Hi mate whats the problem with system ,may be we can help with out the manual

  6. #6
    Join Date
    Mar 2010
    Location
    Bangladesh
    Age
    40
    Posts
    151
    Rep Power
    15

    Re: Trane Chiller Problem

    Thanks for your replay,
    Few days ago our main problem was the chiller unit is tripping frequently, we didnt have any manual to access the fault, now with the help of this forum we have the manual, we can realize the problem, but what will be our steps now?
    Details problem you can find out from my another post (Heading: problem with Trane chiller)
    Our problem: Such as a set point B 02 (Hot water outlet temperature setpoint), B06(Operating mode) showing no value,E 09( evaporator water inlet temp.), E10(Condenser water outlet temp.), E11 (Condenser water inlet temp.) showing no value.

  7. #7
    Join Date
    Apr 2010
    Location
    UK
    Posts
    6
    Rep Power
    0

    Re: Trane Chiller Problem

    Quote Originally Posted by Bashir01219 View Post
    Thanks for your replay,
    Few days ago our main problem was the chiller unit is tripping frequently, we didnt have any manual to access the fault, now with the help of this forum we have the manual, we can realize the problem, but what will be our steps now?
    Details problem you can find out from my another post (Heading: problem with Trane chiller)
    Our problem: Such as a set point B 02 (Hot water outlet temperature setpoint), B06(Operating mode) showing no value,E 09( evaporator water inlet temp.), E10(Condenser water outlet temp.), E11 (Condenser water inlet temp.) showing no value.
    B02, not relevant unless it is a heat-pump
    E09, sensor may not be installed, not a problem as it controls on outlet temperature only
    E10/11, not relevant as it is an air-cooled chiller.

    Are you actually showing a fault on the controller?

  8. #8
    Join Date
    Mar 2010
    Location
    Bangladesh
    Age
    40
    Posts
    151
    Rep Power
    15

    Re: Trane Chiller Problem

    Yes, you r right. Now new fault showing, " A ckt1 HP limit"

  9. #9
    PETER MAHONEY's Avatar
    PETER MAHONEY Guest

    Re: Trane Chiller Problem

    Circuit A has trip out on High Pressure

  10. #10
    Join Date
    Aug 2001
    Location
    Gold Coast, Australia
    Posts
    600
    Rep Power
    28

    Re: Trane Chiller Problem

    G'day Pete. Hurry up & get 15 posts so I can PM you mate.

  11. #11
    Join Date
    Mar 2010
    Location
    Bangladesh
    Age
    40
    Posts
    151
    Rep Power
    15

    Re: Trane Chiller Problem

    i am confused!
    Ckt 1 evaporator pipe is always hot, but ckt 2 evaporator pipe become hot for sometime but not as much as hot like ckt1.
    i know ckt2 start only when ckt1 is not capable, but why its evaporator pipe is not so hot like ckt1.
    And if i touched evaporator coil i can fill negative air pressure or air entering through the coil but in ckt1 evaporator coil there is no such of fillings….why?

  12. #12
    Join Date
    Aug 2001
    Location
    Gold Coast, Australia
    Posts
    600
    Rep Power
    28

    Re: Trane Chiller Problem

    Bashir, here's a direct link to the IOM (manual) for the chiller.
    http://www.trane.com/webcache/rf/scr...e_05011999.pdf
    Also here's a link to the IOM for the SMM controller:
    http://www.trane.com/webcache/rf/scr...e_05011999.pdf
    If you can't fix it with these manuals & your own fridgie skills, then I'm afraid it'll be something that the local Trane service department will most likely need to fix.

    Niether evaporator pipe should be hot when running.
    This machine is a chiller, i.e. it cools water, not air. So I think you're feeling air through the condenser.

    Mate, I'm sorry if this sounds condescending, but if you know so little about the machine you're trying to fix, I'd really recommend you get Trane in to fix it. I'd hate to hear you'd badly injured yourself through a misunderstanding.

  13. #13
    Join Date
    Apr 2010
    Location
    Australia
    Posts
    11
    Rep Power
    0

    Re: Trane Chiller Problem

    is your ckt 1 condenser fan running ????

  14. #14
    Join Date
    Mar 2010
    Location
    Bangladesh
    Age
    40
    Posts
    151
    Rep Power
    15

    Re: Trane Chiller Problem

    Quote Originally Posted by FreezerGeezer View Post
    Bashir, here's a direct link to the IOM (manual) for the chiller.
    http://www.trane.com/webcache/rf/scr...e_05011999.pdf
    Also here's a link to the IOM for the SMM controller:
    http://www.trane.com/webcache/rf/scr...e_05011999.pdf
    If you can't fix it with these manuals & your own fridgie skills, then I'm afraid it'll be something that the local Trane service department will most likely need to fix.

    Niether evaporator pipe should be hot when running.
    This machine is a chiller, i.e. it cools water, not air. So I think you're feeling air through the condenser.

    Mate, I'm sorry if this sounds condescending, but if you know so little about the machine you're trying to fix, I'd really recommend you get Trane in to fix it. I'd hate to hear you'd badly injured yourself through a misunderstanding.

    Sir, we have other chiller unit & lots of engineer to fix problems. But no one is interested to fix this problem.
    Basically the system is running well, ckt1 never shows any problem.
    Problem with the ckt2, it tripped several times in a day due to #High pressure or # low refrigerant in that ckt. We charged it once then for two months it ran well, without any problem, but now it showing the same problems again. Maybe leakage present in that ckt. And tripped due to high pressure because of evaporator fines jam!
    Train local is presently not available in Bangladesh…………..
    We can take help from others (third party), but I want to clear it myself, as long as I am not asking actually I am not learning. Its a problem but also an apportunity for me ...........
    Thank you Sir……….
    Last edited by Bashir01219; 10-05-2010 at 05:25 PM.

Similar Threads

  1. Chiller problem
    By Chiller 09 in forum Commercial
    Replies: 9
    Last Post: 17-12-2009, 03:49 PM
  2. Trane chiller
    By Lman in forum Trouble Shooting
    Replies: 4
    Last Post: 13-11-2009, 03:51 PM
  3. trane rtad 125 chiller, reverse phase issue
    By croc1774 in forum Air Conditioning
    Replies: 5
    Last Post: 25-08-2009, 05:44 PM
  4. Chiller tripping Problem
    By bhasadu in forum Trouble Shooting
    Replies: 0
    Last Post: 21-06-2008, 09:12 AM
  5. Connecting Trane Water chiller to air handling unit
    By celtictech in forum Fundamentals
    Replies: 10
    Last Post: 08-03-2007, 06:14 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •