    Hitachi Set Free problem



    I have a problem with an inverter comp. being locked up and wondered if there is anyone that knows if I could run the second comp. off the inverter.

    The unit is a RAS 10 FSG (inverter comp = 3kw, DOL comp. = 3.7kw) on r407c.

    Any help would be appreciated.

    Thanks


    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  2. #2
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Hitachi Set Free problem

    For Set Free systems there is normally a dip switch setting for disable of compressor function.

    So if you have faulty inverter compressor you can use this dip fuction to stop its operation & in this case the unit will run with only the direct on line compressor or on larger units all of the direct on line compressors.
    Or if you have faulty direct on line compressor you can disable & run only the inverter compressor & or the other direct on line compressors.

    You just choose which compressor you dont want to run.

    Details of this dip setting are in the service manual & on the outdoor unit access panel.

  3. #3
    Join Date
    Feb 2005
    Location
    United Kingdom
    Age
    53
    Posts
    56
    Rep Power
    20

    Re: Hitachi Set Free problem

    I have a manual for this and can get the pages you need to run only the fixed speed compressors. Contact me via the site and I will sort it.

  4. #4
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: Hitachi Set Free problem

    Thanks Imp and Thermatech for your responses and my apologies for the belated reply ( as I've just had some time off ). The new comp turned up that Thursday so the issue became moot.

    Although I would still be interested to know if the inverter has the guts to run the 3.7kw comp.
    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  5. #5
    Join Date
    Feb 2005
    Location
    United Kingdom
    Age
    53
    Posts
    56
    Rep Power
    20

    Re: Hitachi Set Free problem

    the inverter should not be an issue. It is designed to run that compressor. As with any manufacturer inverters are a bit perilous with UK voltages. There was an issue with Hitachi inverters a couple of years back but these were improved with lots of extra protection. Not sure if they applied this to the older FS range though.

Similar Threads

  1. Temperature problem with liquid NH3
    By energeia in forum NH3
    Replies: 34
    Last Post: 05-08-2009, 08:16 AM
  2. Saunier Duval Problem
    By mallorcanangel in forum Air Conditioning
    Replies: 1
    Last Post: 10-07-2009, 01:26 AM
  3. IMI Marstair HLR 540 problem
    By markj in forum Air Conditioning
    Replies: 9
    Last Post: 01-07-2009, 11:07 PM
  4. Well Done / Thanks Hitachi UK
    By Latte in forum Chit Chat & Service Stories
    Replies: 4
    Last Post: 24-11-2008, 07:52 PM
  5. hitachi ducted problems
    By Krups in forum Air Conditioning
    Replies: 16
    Last Post: 01-09-2005, 07:40 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •