I have a copeland scroll compressor motor in a water chiller it is a 2 ton the direction said that I have to have power to the unit 8 hours before turning it on, the problem I have is it is three phase and I run it off of a rotory phase conveter That I would rather not run the phase conveter all night so I can work it the next morning is there any way to hook up a heater on the compressor that I can it on 110 circuit, Thanks
-
21-03-2010, 04:31 PM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: compressor motor heater
Yes it is! You need refrigeration engineer or refrigeration service technician or electrician to that for you!
Heater is already made for 110V 1 phase power supply. If it is not, than it could be purchased.
-
22-03-2010, 12:23 AM #3
Re: compressor motor heater
It is critical that the sump heater is on before operating the compressor. For the fact that the oil in compressor is well above the saturated discharge temperature to elliminate gas saturating into the oil, and problem of oil carry over out of compressor on start up. No oil no lubrication equals dead compressor.
I would respectfully suggest at least 24hours before starting compressor to ensure sump oil temperatures are high. Get a Refrig Technician to sort it out.
-
22-03-2010, 11:17 PM #4
Re: compressor motor heater
Get a separate strap on heater to run off your other power supply.
http://www.springfield-wire.com/cate...CFTOKEN=105215Brian - Newton Abbot, Devon, UK