    Mitsubishi Heavy Industry



    Need help with the following

    Mitsibushi Heavy Industries
    FDKA 301 HES Cassettes

    Customer complaining not enough heat output in Heat mode
    Initiated a test run in cool mode
    Both units ( side by side) showed 50 psi or 5 Bar on Low pressure
    These units are precharged............run is under 7 metres
    Were they perhaps despatched eith less refrigerant charge ??
    R410A

    Second prob

    Systems go in defrost............yet indoor fans continue to run and deliver cold air into room

    Why ??



  2. #2
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Mitsubishi Heavy Industry

    Hi Aiyub,

    Youre's was one of them posts that you read and think thank goodness it isn't one of my call. Sorry i can't help you directly except to say that i have never come accross an easy fault on a mitsi heavy unit. They certainly are not as reliable as the mitsi elec units and every time i have had a fault on one i have ALWAYS ended up having to phone technical for advice. They are weird units and logic doesn't always point you in the right direction. My advice to anyone with a fault on one of these units is unless it is a obvious fault phone for advice. I thought i had a direct phone number for mhi technical but can't find it at the moment. it might be worth rining 1st distribution or 3D and ask their guys (They are the one;s that sell these unit)

    Sorry i can't help any further

    Regards

    Fatboy

  3. #3
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25

    Re: Mitsubishi Heavy Industry

    Aiyub, i.m not really a fault finding guy but i'll try.

    On a 410a system in this weather i would expect, maybe, to see 5 bar(75ish psi) on the low side, but not 50psi (3.5ish bar).

    Me personally, not being a technical man, would be inclined to reclaim, weigh and see if shortage of gas is the problem.
    For the couple of kg or so of gas, verses the hours of thinking about it it. i would check it out.
    If it wasn't this, and you agreed with the customer that not enough heat was being produced, i agree with rdocwra ring up 3dair.
    Well that was before HRP took over, now i would flog them something new.

    As for the cold air on de-frost. The crappy samsung bionizer in my daughters bedroom does the same, nuff said.

    Cheers

    eggs

  4. #4
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Mitsubishi Heavy Industry

    Quote Originally Posted by Aiyub
    Need help with the following

    Mitsibushi Heavy Industries
    FDKA 301 HES Cassettes

    Customer complaining not enough heat output in Heat mode
    Initiated a test run in cool mode
    Both units ( side by side) showed 50 psi or 5 Bar on Low pressure
    These units are precharged............run is under 7 metres
    Were they perhaps despatched eith less refrigerant charge ??
    R410A

    Second prob

    Systems go in defrost............yet indoor fans continue to run and deliver cold air into room

    Why ??
    G'day Aiyub.
    Had a heavy industries unit blowing cold air on heating at times,it was a wall mounted split.The indoor fan always ran on heating even if the compressor wasn't running.(No hot start.)They came from the factory like this

    The indoor unit has dip switches on the pcb which you can change so the indoor fan cycles with the compressor.This may or may not be applicable to your model.

    The customer had recently complained of the fan continuing to run even when the unit was on defrost, but wasn't asking for immediate attention because it's summer at present.But my bet is that the dip switches may be able to change this as well.I would be interested to hear what you find.

    Good luck.

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Mitsubishi Heavy Industry

    Hi Abe,

    So as my Sanyo Ergo mini split.
    The indoor fan, runs at all times but very slow on defrost and heating mode when compressor stops.

    May be change the vane direction so the people in the room will not feel the cold draught.

    Chemi

  6. #6
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Mitsubishi Heavy Industry

    Temprite

    I rang technical today.............This is what they said. On a defrost, approx once an hour the fan shuts off and the indoor coil goes into cooling mode.

    Then the fan starts up for a while and blows air into the room through the iced up coil. ( strange that I say)) surely the fan should only come on once the indoor coil reaches a certain temperature

    Customer says it blows cold for about 15 mins...........I says surely cant be that long.

    MIt say that the weather conditions we have at present..........wet damp snow with high RH, are the worst possible conditions for Heat pump mode.

    I think your dip switch solution is probably the case.

    Im going to ask them tomorrow if its possible to adjust a dip switch on indoor unit so fan cycles goes off..............

    Adjusting Vane

    I cannot do that. Cassette is slung high on ceiling...........within a void...............air flow has to point straight down............

    If I adjust position it will blow into a void within the ceiling..........but thx for the tip.

    Im there 2moro afternoon.........spending a few hours there monitoring.....................I hate going back to a job..........

    Sigh..............Wish Id stuck with LG!!!!!!!!
    Last edited by Abe; 24-02-2005 at 06:46 PM.

  7. #7
    rbartlett's Avatar
    rbartlett Guest

    Re: Mitsubishi Heavy Industry

    Quote Originally Posted by Aiyub

    Sigh..............Wish Id stuck with LG!!!!!!!!
    no you don't

    been installing some LG 10kw wall/ceiling convertables..what a heap of sh...

    the customer asked to day if they were noisey...I almost replied 'only if you turn them on'.....

    cheers

    richard

  8. #8
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Mitsubishi Heavy Industry

    and then check
    the length of the pipe if it is more than it is precharged
    add about 25 g per extra meter boss
    Are you guessing?

Similar Threads

  1. Mitsubishi problem
    By marc5180 in forum Trouble Shooting
    Replies: 15
    Last Post: 17-01-2007, 10:06 PM
  2. Mitsubishi heavy industrial A/C.
    By Langer in forum Air Conditioning
    Replies: 10
    Last Post: 14-08-2006, 11:31 AM
  3. Mitsubishi Heavy Industries HELP
    By Bakerbj in forum Air Conditioning
    Replies: 10
    Last Post: 26-07-2006, 03:18 PM
  4. MITSUBISHI Heavy Industries
    By coolit24 in forum Air Conditioning
    Replies: 8
    Last Post: 06-03-2006, 08:46 AM
  5. Mitsu Heavy Industry
    By bobjob in forum Air Conditioning
    Replies: 1
    Last Post: 14-07-2005, 11:00 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •