    PED & Relief valve advice sought



    Hello,
    First post here so please be gentle
    Have done some research & think I have a reasonable understanding but reading through all the regulations etc is very heavy going so am hoping for some confirmation ;
    If I have 'created' a 'pressure vessel/system' by connecting a remote condenser using pipework with a max allowable working pressure ( say 20 bar), should my pressure test be 20 x 1-43?
    Also, what should the lift setting on my safety valve be; assuming correct sizing for exhaust ( is it 10% above max working pressure)?



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: PED & Relief valve advice sought

    The pressure test is right at x1.43 times the PS, but the safety valve must be set at any value lower than the PS, including the max positive tolerance of the blow off. E.g. if the valve has a tolerance of +1/-2 bar from the stamped value, you have to buy a 19 bar safety valve.

  3. #3
    Join Date
    Mar 2010
    Location
    europe
    Posts
    14
    Rep Power
    0

    Re: PED & Relief valve advice sought

    Hi NoNickName,
    Surely the relief wil e above the 'max working pressure' or then you never can achieve max working pressure as we will have lifted the relief?

  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: PED & Relief valve advice sought

    The PS is the max allowable pressure. There is no such a "max working pressure". The whole 97/23/EC directive doesn't contain the word "working".
    And surely the relief valve must be set BELOW that value.
    The test pressure must be set in accordance with the PS.

Similar Threads

  1. Replies: 3
    Last Post: 26-08-2009, 09:37 AM
  2. LEV does not open
    By Yuri B. in forum Air Conditioning
    Replies: 7
    Last Post: 19-07-2009, 02:37 PM
  3. Oversize Relief Valve
    By Dacosta in forum NH3
    Replies: 1
    Last Post: 05-09-2008, 11:35 AM
  4. Carbo Cooler relief valve
    By flasah in forum NH3
    Replies: 2
    Last Post: 24-06-2006, 09:31 AM
  5. Relief Valve on Suction
    By Latte in forum Commercial
    Replies: 19
    Last Post: 20-01-2004, 11:57 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •