    Problems in CBP compressor cooling unit



    Dear friends,
    We have designed a chiller unit with a Tecumseh CBP compressor, rating 750 BTU. Of the three machines, one machine is working fine. Other two machines are taking too long to cool. I have replaced the synthetic oil in the compressor with mineral oil as we are using hydro carbon as refrigerant. The variation in the parameters are as follows

    Discharge line temp in OK machine = 65 deg Centrigrade immediately within 5 secs
    Discharge line temp in problematic machine = 40 deg after 10 mins

    Condenser air flow temp in OK machine = 42 Deg
    Condenser air flow temp in problematic machine = 30 Deg

    What I could understand is that the system is not throwing out enough heat, but could understand where is the problem.

    Please suggest trouble shooting options

    Thanks and regards
    Giridhar



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Problems in CBP compressor cooling unit

    Install some access valves and measure high and low pressure, temperatures of pipes after evaporator and condenser, discharge pipe, suction pipe near compressor and before expansion device, condenser air in and out temperature, water in and out temperature and give us full compressor model# and compressor current. Also, tell us what is refrigerant used.
    Then we will probably know what is happening since we cannot be fisically there to see, touch, smell, hear and do that measurement instead of you.

    Or we could guess like blind chickens in sand looking for worm and tell you that machine probably doesn't getting enough heat from evaporator or capillary clogged or something else.
    So, give us full measurements!

    Did you changed oil in all 3 units or only in problematic one. If later is case, you may have problem with mixing oils vax formation or oil viscosity.
    Last edited by nike123; 19-03-2010 at 01:41 PM.

Similar Threads

  1. Carrier Transicold Container Problem
    By Shamel in forum Transport
    Replies: 39
    Last Post: 23-01-2012, 11:23 PM
  2. Water leak on a daikin wall unit
    By marc5180 in forum Air Conditioning
    Replies: 5
    Last Post: 27-08-2009, 07:23 PM
  3. Mitsi Electric Wall Unit Switching Off
    By marc5180 in forum Air Conditioning
    Replies: 16
    Last Post: 26-07-2009, 10:02 PM
  4. New Toshiba unit won't start..?
    By expat in forum Air Conditioning
    Replies: 14
    Last Post: 07-04-2008, 09:11 PM
  5. SL/SB-400 Pump Down Procedures
    By absolute-zero in forum Transport
    Replies: 1
    Last Post: 29-01-2008, 09:27 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •