    9000btu split



    hi guys,
    i have a 9000btu split unit returned to me by a customer, the unit ran for a while it seems, customer complaint not pumping.

    when i opened the unit it seems the compressor got hot due to stickers melted on compressor, when i turn on the unit, the compressor makes a loud buzzing noise then kicks out but does not trip the board, the fan still works, when i turn the unit off, you can hear a click from the compressor.

    what could cause this to happen to the compressor apart from over heating? insufficient gas, too much gas or liquid in th system?



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: 9000btu split

    Cheap compressor, running without or not enough refrigerant, bad elactrical connections, air in the system.

  3. #3
    Join Date
    Oct 2008
    Location
    Australia
    Posts
    210
    Rep Power
    16

    Re: 9000btu split

    The click is the overload on the compressor.

Similar Threads

  1. How good is your split system running?
    By acnerd in forum Air Conditioning
    Replies: 18
    Last Post: 05-08-2009, 07:35 PM
  2. Replies: 18
    Last Post: 15-04-2009, 08:42 PM
  3. Sensible Heat Factor / capacity of Inverter split Systems at part load?
    By Greengrocer in forum Technical Speculations
    Replies: 31
    Last Post: 09-02-2009, 04:57 PM
  4. Australian split installers, some info needed
    By paul_h in forum Air Conditioning
    Replies: 10
    Last Post: 20-05-2008, 03:40 PM
  5. Do you beleive in data of split units?
    By jirhol in forum Fundamentals
    Replies: 4
    Last Post: 29-03-2008, 11:17 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •