    Retrofitting R22 In a split system



    I've been called to a job tomorrow that is faulting on "LP", luckily we can still get hold of reclaimed R22 from the suppliers but i'm wondering has anyone relaced R22 yet in a split system and if so what have they used? and is it a direct replacement.

    Everyone that i ask doesn't seem to know and as of yet we haven't had to retrofit any.


    The difference between genius and stupidity is that genius has its limits.

    Marc

  2. #2
    Join Date
    May 2006
    Location
    Isle of Wight, Uk
    Age
    47
    Posts
    424
    Rep Power
    20

    Re: Retrofitting R22 In a split system

    Tried some R417a in a crappy old hitachi wall mount split, pressures were low - pressure was always low, before the leak, even on the R22. So can't really give you much info. Hopefully next time I use it, it will be on a more modern unit with a bit more quality to start with.
    Andy

  3. #3
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    239
    Rep Power
    19

    Re: Retrofitting R22 In a split system

    yea have been using r417a as a replacement and it seems to be fine, have found it usaly runs around 50 - 60 on the suction

    417 for cappillary device
    422 for expansion valve

    agas have a good sheet out on what replaces what etc
    Last edited by thebigcheese; 16-03-2010 at 10:24 PM.

  4. #4
    Join Date
    Dec 2008
    Location
    UK
    Posts
    564
    Rep Power
    24

    Re: Retrofitting R22 In a split system

    R417A seems to work fine in split A/C systems. I have found that you often need to charge to about 90% by weight of refrigerant when compared to the R22 quantity. You might need to trim this charge amount slightly, but start at 90%. Pressures appear to be similar to R22, maybe slightly lower, but achieved temperatures seem to be OK.

  5. #5
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Retrofitting R22 In a split system

    Good stuff, i'm prepared now when R22 runs out, thanks.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  6. #6
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Retrofitting R22 In a split system

    Any luck with 417 in a pack? Is it a good option as say converting to 404a?

    Alec

  7. #7
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    239
    Rep Power
    19

    Re: Retrofitting R22 In a split system

    al we have been using 422d for most refrigeration aps, seems to be ok

    aparently r407a is great if you can do an oil change

  8. #8
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Retrofitting R22 In a split system

    My only worry with the oil change is o rings leaking, otherwise i'd go with 404a.

    alec

  9. #9
    Join Date
    Dec 2009
    Location
    Spain
    Age
    45
    Posts
    229
    Rep Power
    15

    Re: Retrofitting R22 In a split system

    If you change directly to 417a and not change the oil, you will also have lubricity problems, as it is not very miscible with the MO. Only 3% of it is a HC, miscible with MO, whereas 97% is a HFC.
    A nice solution would be to clean the circuit out of MO and put 407 and POE. BEsides, you can earn some COP and CAP with the total cleaning of the plant.
    check this link:
    www.fri3oilsystem.com/june.zip
    there you have the different retrofit options, so you can decide which one is more suitable for you.

  10. #10
    Join Date
    Nov 2009
    Location
    Poland
    Posts
    82
    Rep Power
    15

    Re: Retrofitting R22 In a split system

    I use R407C only mention on the synthetic oil and filter change (as is) no flushing system, and possibly if it is long and it is suspected that there remained a mineral oil, possibly under pressure of nitrogen blows.

  11. #11
    Join Date
    Dec 2009
    Location
    Spain
    Age
    45
    Posts
    229
    Rep Power
    15

    Re: Retrofitting R22 In a split system

    If you leave over 5% of remaining MO, you will end up having a phases separation, and a damage of the lubricity index, that will finally break the compressors, specially if there is a leak.
    So the best solution is to clean entirely the system.

Similar Threads

  1. Installation question split system
    By jom2000 in forum Air Conditioning
    Replies: 6
    Last Post: 16-05-2009, 01:17 PM
  2. steps on tonnage calc for split system
    By Jimmy.Thurman in forum Fundamentals
    Replies: 1
    Last Post: 05-05-2009, 11:27 PM
  3. Recommendation for small split system that will cool to 16 degrees ?
    By cool burn hurt in forum Air Conditioning
    Replies: 13
    Last Post: 16-09-2008, 08:24 PM
  4. Highcool Split system
    By HOTROV in forum Air Conditioning
    Replies: 10
    Last Post: 05-07-2007, 07:51 AM
  5. Replies: 5
    Last Post: 22-06-2005, 07:41 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •