    Fujitsu Multi ~ reduce 3 circuits to two



    A customer has an existing multi-system, involving one condenser AOY30LMAW4 (R410a, nominal cooling capacity 8kW) with three 2.8kW wall-mounted room units connected.

    The plan is to remove one of those circuits, leaving just the two room units connected to the multi-condenser.



    Would the system work happily wth just the two circuits? Any downside/worries?



  2. #2
    Join Date
    May 2006
    Location
    Sussex
    Posts
    362
    Rep Power
    20

    Re: Fujitsu Multi ~ reduce 3 circuits to two

    Answering my own question, now, having done some phoning around, seems the min capacity of the system is 7.9kW (nomimal), which means it will not be happy on just the two circuits, them being less than 7.9kW.

    Drats.

  3. #3
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: Fujitsu Multi ~ reduce 3 circuits to two

    Quote Originally Posted by Makeit go Right View Post
    Answering my own question, now, having done some phoning around, seems the min capacity of the system is 7.9kW (nomimal), which means it will not be happy on just the two circuits, them being less than 7.9kW.

    Drats.
    If its an inverter it will be fine I would have thought.

    it will vary its output based on the load.

    You might have 3 units connected at the moment but you could run just one of those if you wished.

    Usually they state that you should have at least 2 units connected in total but whether you use both units or not it doesnt matter.

    The nominal is just the rated output. It would be fine to have just 2 units connected.

  4. #4
    Join Date
    Aug 2008
    Location
    uk
    Posts
    22
    Rep Power
    0

    Re: Fujitsu Multi ~ reduce 3 circuits to two

    i would add that you should be careful running too much under capacity, the resultant reduction in refrigerant could increase compressor temp, and the likelihood of failure, if you do go ahead monitor the comp shell temps to see if this is a problem

  5. #5
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: Fujitsu Multi ~ reduce 3 circuits to two

    Quote Originally Posted by Haden4ever View Post
    i would add that you should be careful running too much under capacity, the resultant reduction in refrigerant could increase compressor temp, and the likelihood of failure, if you do go ahead monitor the comp shell temps to see if this is a problem
    The units will be designed to have only one unit in operation but there will be a minimum number of units that you can have in operation.

    I run my multi split with 1 unit running much of the year as once the other rooms come upto temperature they stay at that temp all day. Only in extremes of summer/winter do they all need to be running.

    If your worried check with the manufacturer.

  6. #6
    Join Date
    Jul 2008
    Location
    Australia
    Age
    76
    Posts
    21
    Rep Power
    0

    Re: Fujitsu Multi ~ reduce 3 circuits to two

    The unit will not work with only 2 heads. The microchips should be programmed to show a fault if only 2 heads are connected. Also a liquid reciever may be needed (std Fujitsu part) with 3 2.8kw heads. It does'nt matter if you use only 1 head as long as 3 or more are connected.

  7. #7
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: Fujitsu Multi ~ reduce 3 circuits to two

    Quote Originally Posted by Robin View Post
    The unit will not work with only 2 heads. The microchips should be programmed to show a fault if only 2 heads are connected. Also a liquid reciever may be needed (std Fujitsu part) with 3 2.8kw heads. It does'nt matter if you use only 1 head as long as 3 or more are connected.
    This must be unique to fujitsu as other multisplit systems you can usually add "upto" 3 units meaning you can have whatever you want connected.

Similar Threads

  1. Fujitsu Multi problem
    By BMS1 in forum Heat Pumps
    Replies: 15
    Last Post: 02-09-2010, 06:41 AM
  2. Fujitsu AOY90TPAMF
    By andy c in forum Heat Pumps
    Replies: 6
    Last Post: 08-02-2010, 04:22 PM
  3. fujitsu multi split, how it works??
    By 123-steve909 in forum Air Conditioning
    Replies: 9
    Last Post: 04-06-2009, 07:07 AM
  4. fujitsu wall mount volt free relay
    By mike live in forum Air Conditioning
    Replies: 3
    Last Post: 09-04-2009, 08:26 PM
  5. Fujitsu multi issue
    By chillymatt in forum Air Conditioning
    Replies: 10
    Last Post: 11-01-2009, 02:58 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •