    Do people use their manifold gauges for strength testing or do you have a separate high pressure gauge just for this job?
    If so what gauge do you use ?
    Is it OK to use any high pressure gauge ?
    Oct 2008
    mallorca, spain,
    75
    768
    Re: manifold gauge
    have you a nitrogen bottle regulator?
    it would be better to use this
    Mar 2007
    45
    78
    Re: manifold gauge
    I do have a nitrogen regulator ,but if I had a 10 psig drop over 1 hour or so the gauge would not be accurate enough to show the drop.
    For example. when I have a leak on a vrv I pressure test and shut the service valves and attach 1 gauge to the condensor and 1 gauge to the pipe work and leave it over night. To do this I use 2 sets of gauges.
    Sep 2003
    ISRAEL
    72
    4,248
    Re: manifold gauge
    Use 410 high side gauge.
    Look for the biggest you can find, its the most accurate.
    Sep 2009
    Scotland
    374
    Re: manifold gauge
    Quote Originally Posted by robin r33 gtr View Post
    A proper pressure testing rig should be used for strength testing 410a (40bar) these are readily available from most suppliers.
    I use a Javac rig
    http://www.javac.co.uk/nitrogen-pressure-regulator-uk-c-302-p-1-pr-16242.html
    Oct 2003
    5,630
    34
    Re: manifold gauge
    You can use a 1-way manifold like this or use just thus the dial without a valve on it. I never leave a manifold on the system while testing for leaks.
    A good technique nowhere explained in books: you pressurize the system with a full nitrogen bottle till everything stabilizes on the desired pressure.
    You have your pressure regulator which will show you let's say 25 bar on you system side (LP side) and 150 bar on the OFN side (HP side).
    The LP side is a small pressure but big volume compared to the HP side with its high pressure and very small volume( only the pressure diaphragm in the regulator)
    You close only the valve on the OFN bottle and let the pressure on the regulator.
    We have the Gas law (Boyle) which states P x V = ct
    So the smallest leak on the LP side will drop the pressure very fast on the HP side because the regulator will try to maintain pressure but there's no volume to do this, so HP will drop and drop very fast. Try once.
    Mar 2007
    45
    78
    Re: manifold gauge
    Thanks for all the help.
    3,856
    Re: manifold gauge
    I have a single gauge one like Peter showed made by refco.
  1. Manifold Gauge and Hose question
    By lees8110 in forum Air Conditioning
    Last Post: 10-06-2009, 10:51 PM
  2. Troubleshooting a vacuum pump and gauge set.
    By Old Codger in forum Fundamentals
    Last Post: 08-08-2008, 05:13 PM
  3. CPS Manifold gauge ports
    By JD-SMART-REPAIR in forum Trouble Shooting
    Last Post: 15-06-2008, 06:55 PM
  4. Safe pressure testing with gauge manifold
    By alexdouglas1969 in forum Fundamentals
    Last Post: 16-09-2007, 04:37 AM
  5. Gauge Manifold Sets
    By Derek in forum Technical Discussions
    Last Post: 12-07-2005, 09:06 AM