    Dear All,
    I started one screw compressor that is designed in condition -10 C as evaporating temp. and +35 as condensing temp. also this compressor is designed with fixed Vi
    The pressure of liquid seperator (suction press) was 7 bar(a) in start.
    The compressor worked at partial load (about 10% capacity) about 5min. after that high discharge temp. alarm turned up.
    I think inner pressure of compessor at oil input of compressor has extra pressure rather discharge press. so oil circulation not been did correctly.
    Please advise if you have idea
    3,357
    Re: oil cooling problem
    chichi ,
    If compressor is differential oil feed it may cause this due to low oil flow, because little pressure difference between suction & discharge .
    If lubricated and oil injection cooling by oil pump it should work fine .
    Either load machine up or restrict suction valve on machine to achieve bigger pressure difference until plant settles down .
    iran
    45
    36
    thanks a lot for your kind advice
    iran
    45
    36
    chichi ,
    Jan 2006
    Croatia
    68
    2,261
    31
    Hi, chichi
    Quote Originally Posted by chichi View Post
    Dear All,
    sometimes at very low partial load you can have a high oil temp .... RANGER1 gave you a good suggestion ... the best is to increase capacity a little to achieve more refrigerant to flow through compressor in your case suction gas had a very high temperature and flow was reduced - right way to get high oil temp ....(take care not to come to high discharge pressure)
    Best regards, Josip
  1. Liebherr fridge sounds, cooling and LCD problem
    By bv1976 in forum Trouble Shooting
    Last Post: 03-03-2010, 11:31 AM
  2. Cooling problem with VRV REYQ24M7.
    By cool#9 in forum Air Conditioning
    Last Post: 07-02-2010, 12:20 PM
  3. LG heat pump problem
    By back2space in forum Heat Pumps
    Last Post: 01-02-2009, 11:23 PM
  4. Furance problem
    By ALONEI in forum Trouble Shooting
    Last Post: 14-05-2008, 11:32 AM
  5. Regulation of cooling capacity
    By npaisnel in forum Domestic
    Last Post: 08-02-2002, 11:22 PM