    oil cooling problem



    Dear All,

    I started one screw compressor that is designed in condition -10 C as evaporating temp. and +35 as condensing temp. also this compressor is designed with fixed Vi
    The pressure of liquid seperator (suction press) was 7 bar(a) in start.
    The compressor worked at partial load (about 10% capacity) about 5min. after that high discharge temp. alarm turned up.
    I think inner pressure of compessor at oil input of compressor has extra pressure rather discharge press. so oil circulation not been did correctly.
    Please advise if you have idea



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: oil cooling problem

    chichi ,

    If compressor is differential oil feed it may cause this due to low oil flow, because little pressure difference between suction & discharge .

    If lubricated and oil injection cooling by oil pump it should work fine .

    Either load machine up or restrict suction valve on machine to achieve bigger pressure difference until plant settles down .

  3. #3
    Join Date
    Dec 2007
    Location
    iran
    Age
    45
    Posts
    36
    Rep Power
    0

    Re: oil cooling problem

    thanks a lot for your kind advice

  4. #4
    Join Date
    Dec 2007
    Location
    iran
    Age
    45
    Posts
    36
    Rep Power
    0

    Re: oil cooling problem

    Quote Originally Posted by RANGER1 View Post
    chichi ,

    If compressor is differential oil feed it may cause this due to low oil flow, because little pressure difference between suction & discharge .

    If lubricated and oil injection cooling by oil pump it should work fine .

    Either load machine up or restrict suction valve on machine to achieve bigger pressure difference until plant settles down .
    thanks a lot for your kind advice

  5. #5
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: oil cooling problem

    Hi, chichi

    Quote Originally Posted by chichi View Post
    Dear All,

    I started one screw compressor that is designed in condition -10 C as evaporating temp. and +35 as condensing temp. also this compressor is designed with fixed Vi
    The pressure of liquid seperator (suction press) was 7 bar(a) in start.
    The compressor worked at partial load (about 10% capacity) about 5min. after that high discharge temp. alarm turned up.
    I think inner pressure of compessor at oil input of compressor has extra pressure rather discharge press. so oil circulation not been did correctly.
    Please advise if you have idea
    sometimes at very low partial load you can have a high oil temp .... RANGER1 gave you a good suggestion ... the best is to increase capacity a little to achieve more refrigerant to flow through compressor in your case suction gas had a very high temperature and flow was reduced - right way to get high oil temp ....(take care not to come to high discharge pressure)

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

Similar Threads

  1. Liebherr fridge sounds, cooling and LCD problem
    By bv1976 in forum Trouble Shooting
    Replies: 0
    Last Post: 03-03-2010, 11:31 AM
  2. Cooling problem with VRV REYQ24M7.
    By cool#9 in forum Air Conditioning
    Replies: 3
    Last Post: 07-02-2010, 12:20 PM
  3. LG heat pump problem
    By back2space in forum Heat Pumps
    Replies: 132
    Last Post: 01-02-2009, 11:23 PM
  4. Furance problem
    By ALONEI in forum Trouble Shooting
    Replies: 10
    Last Post: 14-05-2008, 11:32 AM
  5. Regulation of cooling capacity
    By npaisnel in forum Domestic
    Replies: 13
    Last Post: 08-02-2002, 11:22 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •