    Pipework Flushing



    We've got a site where we are about to change 2 cassette systems operating on R22 to new systems operating on R407C.

    Due to the length of the pipework runs and the difficulty factor in replacing the pipework we are considering re-using the pipework and have looked at using a flushing agent.

    Has anyone got any experience of this? any tips appreiciated.



  2. #2
    Join Date
    Dec 2004
    Location
    LEBANON
    Age
    44
    Posts
    854
    Rep Power
    21

    Re: Pipework Flushing

    well we used to flush systems with R22 , i donno about another agents , more information will be appreciated
    Engineering, sciences, math, physics and my brain will generate "not responding " soon

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Pipework Flushing

    Hi Frank,

    I have written here something about a flushing agent.
    It will be faster to go to the shop and read the lable then find the post.

    I'll be back soon.

    Chemi

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Pipework Flushing

    It finnished and gone.

    The original was R 114 and R 11 so there are many replacements on the market.

    Got one for you and I'm sure it will do the job just fine
    http://www.honeywell.com/sites/sm/ch...lv/ACFlush.htm

    Chemi

  5. #5
    Join Date
    Jan 2003
    Location
    Crewe, United Kingdom
    Age
    58
    Posts
    723
    Rep Power
    22

    Re: Pipework Flushing

    For automotive work I used to use brake parts cleaner to remove mineral oil when doing a retrofit. I used a one litre pressurised bottle, and force it through at 80 or 90 psi, then I used to pass plenty of nitrogen through to ensure that all the cleaner evaporates.

    I have recently built a closed loop flushing machine using an old robinair recovery unit which basically forces your choice of refrigerant (In my case R134a) through the system using the push pull method, but passing the returning refrigerant (and contaminants) through a disposible automotive reciever drier before the vapour is returned to the storage tank, via an oil separator. Seems to me that you could use the similar idea on domestic a/cs, if you join the two ends of the pipework at one end then you can form a closed loop and flush away.

    Hope that this helps
    Karl

  6. #6
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25

    Re: Pipework Flushing

    Frank, we installed 2 Mitsubishi electric cassettes, specially made for this kind of job.
    Just give them the first service a couple of weeks ago. Fine, running great.
    If you havn't heared of them, i'll find out which models they were tomorrow, from my sidekick.

    Cheers


    eggs

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Pipework Flushing

    These units has a special filters mounted in it. You let them run first some days on this special filter and via the shut off valves, you then switch to the other circuit.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  8. #8
    Join Date
    Feb 2005
    Location
    london
    Posts
    32
    Rep Power
    0

    Re: Pipework Flushing

    mitsubishi power inverters are specially built for this
    use the dip swithes for the first few hours then reset
    this remove all the s### from the system

  9. #9
    Join Date
    Dec 2001
    Location
    UK
    Posts
    137
    Rep Power
    23

    Re: Pipework Flushing

    If you are replacing the units with R407C units but wish to reuse the pipework then you need to flush the pipework out with a suitable flushing agent such as Endoflush to remove all traces of the mineral oil.
    This is usually pumped around the system so it would be as well to leave the evaporator attached untill afterwards.
    Alternatively and with a lot more hard work you could change the oil in the current compressor before changing the system. leave it running for a week then rechange the oil. once the mineral oil concentration is below 5% then change the system.
    To check the concentration you would need to get a test kit from your supplier and take a sample which you then send off.
    The R407C system can cope with a maximum of 5% mineral oil in the polyolester oil.

    BritCit_Juve

  10. #10
    Join Date
    Aug 2009
    Location
    Turhona.libya
    Posts
    79
    Rep Power
    15

    Re: Pipework Flushing

    I would imagine that the pipes which you want to reuse them are still the correct size for the new installations.if they are so i would advice you to use Rx11 the new replacment for R11 which now being band and was using in such flush.

Similar Threads

  1. Flushing oil from a system.
    By djbe in forum Commercial
    Replies: 11
    Last Post: 26-06-2006, 02:20 PM
  2. Eathanol As a flushing Agent
    By Mastercool in forum Technical Speculations
    Replies: 14
    Last Post: 06-06-2006, 09:34 PM
  3. Pipework cleaning up (Inside)
    By Latte in forum Air Conditioning
    Replies: 6
    Last Post: 22-10-2005, 05:55 PM
  4. System flushing
    By Mickvee in forum Air Conditioning
    Replies: 10
    Last Post: 18-09-2005, 07:20 PM
  5. Porus pipework
    By Latte in forum Supermarket Refrigeration
    Replies: 17
    Last Post: 05-04-2005, 11:55 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •