    Evasive gas leak



    I have finally found and repaired a gas leak which I found on the 5/8 soft drawn copper pipe liquid line of a freezer room.
    The gas was sprayng out of a pin hole in the 90 degree bend of the tube.
    This bend was formed with a pipe bender.
    There were no welds where the leak developed and it was not possible that someone could have physically damaged the pipe. There was no vibration or any stress on the pipe.
    The system has been leak free for 5 years.
    The refrigerant is 507.
    In my efforts to trace this leak I used almost every leak detection method I am aware of without success.
    My success rate of tracing a leak in all other systems has been 100% at the first attempt so you can imagine my frustation when I was not able to trace this evasive leak.

    How is it that a leak developes like this for no apparent reason and only leaks under circumstances when you are not on site?

    Any one have a similar experience?

    Cheers,
    Feeze



  2. #2
    Join Date
    Dec 2004
    Location
    Romania
    Age
    58
    Posts
    66
    Rep Power
    20

    Re: Evasive gas leak

    Last year (2004)has-been for me the'' year of leak''.i have 4 same fault, 1 open dispay cabinet 2 auto AC , 1 a small coldroom.I hope that kind of fault will pass beside me, this year .
    what quantity of refrigerant has-been in this plant ? in how many time did he lose the refrigerant?

  3. #3
    Join Date
    Jan 2004
    Location
    South Africa
    Posts
    71
    Rep Power
    21

    Re: Evasive gas leak

    The system takes about 10 kg 507.
    The system had to be toped up with 5kg every 7th day.
    Today is the 10th day since fixing the leak and I have not had a call out so I am on the verge of celebrating but I still have to climb the hurdle of invoicing the customer.
    Cheers,
    Feeze

  4. #4
    Join Date
    May 2004
    Location
    england
    Age
    61
    Posts
    48
    Rep Power
    0

    Re: Evasive gas leak

    once in a large supermarket I had a whole length of suction line on top of a cold store that was setting off the parracense leak detection system. The copper had seemed to become pourus with lots of microscopic holes. has any one else ever come across this before?

  5. #5
    Join Date
    Jan 2004
    Location
    South Africa
    Posts
    71
    Rep Power
    21

    Re: Evasive gas leak

    Dill,
    This leak also occured on the the roof of the freezer room but it was on the liquid line. Once when the building was still new there was a leak from the roof of the building.
    The rain water fell on the piping at the point of the leak.
    I am wondering if this was perhaps a catalyst in starting a reaction- just grasping at straws.
    Cheers,
    Feeze

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Evasive gas leak

    The best practise to detect those small pinhole leaks is to evacuate the refrigerant, top it with OFN + helium and use soap.

    In closed places, the electronic gadgets go wild.

    Holes in copper tubes, indicates low copper quality.

    Chemi

  7. #7
    Join Date
    May 2004
    Location
    southern england
    Age
    69
    Posts
    86
    Rep Power
    20

    Re: Evasive gas leak

    Hi Feeze, good job you don't work in the uk, as your addmission to topping up systems would bring you into conflict with the Enviromental protection act. Possible £20,00.00 fine and / or inprisonment ???. Problem sainsburys had with large copper pipe some time ago was 1) the quality of the pipe and 2) installing engineers useing scented talcum powder to slip insulation onto pipe. This reacted with moisture and attacked the surface of the copper. Most good installers now use french chalk to ease installation of insulation.
    it's only a fridge, fix it. ;)

  8. #8
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Evasive gas leak

    A Little trick with slipping the insulation on,

    I use a wide (50mm) insulation tape on the pipe and then slip on the insulation.
    Works like Vaseline in other activities

    Chemi

  9. #9
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,482
    Rep Power
    21

    Re: Evasive gas leak

    once in a large supermarket I had a whole length of suction line on top of a cold store that was setting off the parracense leak detection system. The copper had seemed to become pourus with lots of microscopic holes. has any one else ever come across this before?
    hi dill

    i have also came across this situation but my boss`s won`t beleive me, but im glad to here of it elsewhere cos i was starting to doubt myself
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  10. #10
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Cool Re: Evasive gas leak

    Quote Originally Posted by Feeze
    The system takes about 10 kg 507.
    The system had to be toped up with 5kg every 7th day.
    Today is the 10th day since fixing the leak and I have not had a call out so I am on the verge of celebrating but I still have to climb the hurdle of invoicing the customer.
    Cheers,
    Feeze
    Hello Feeze.
    Did your electronic leak detector go off when you were trying to find this leak.It must have been going crazy.

    I got called to a system once that another company had been putting about 5kg every 10 days into for approx 6 months.It was into a pub system.Leak wasn't too hard to find.I walked onto the front doors of the pub with the detector turned on.It went nuts.

    I use a Javac tek mate.But even though it says for use with r134a.I sometimes have leaks that you can see with soap,but the detector hardly goes off unless you are right on top of the leak with r 134a.Anyone else have this kind of problem?

    Regards.

  11. #11
    Join Date
    Jan 2004
    Location
    South Africa
    Posts
    71
    Rep Power
    21

    Re: Evasive gas leak

    Temprite,
    Yes, the leak detector did go crazy when I walked in the shop,
    but only on the last time when the leak was visibly spraying out.
    I have a D-Tek electronic leak detector which can detect most
    refrigeration gasses. I have had lots of successful stories with it.
    I also used the ultrasonic method, the ultraviolet dye method and the soap bubble method on this system.
    I found other minor leaks on this system while searching for the main culprit. These I repaired thinking that they may have been the cause of the gas shortage but to no avail, the culprit remained hidden. Any one else would have walked away from this problem but I persivered, I refused to allow myself to be beaten. As someone else on the forum said " Its only a fridge- fix it"
    Cheers,
    Feeze

  12. #12
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Evasive gas leak

    installing engineers useing scented talcum powder to slip insulation onto pipe. This reacted with moisture and attacked the surface of the copper. Most good installers now use french chalk to ease installation of insulation.
    I hope this isn't true as we tend to use "Johnsons Baby Powder" when we experience hard to install armaflex

  13. #13
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Evasive gas leak

    I hope this isn't true
    Might, or might not but sure is, smell's better

    Chemi

  14. #14
    Join Date
    Feb 2005
    Location
    london
    Posts
    32
    Rep Power
    0

    Re: Evasive gas leak

    ultra sonic leak detector are thay any good
    i have benn thinking of buying 1 ????????????

  15. #15
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Evasive gas leak

    I have one, don't do it.
    They're in py opinion made for other purposes.

    Frank, we use exactly he same powder from Johnson, but last month, we forgot the bottle at home and bought some chalk in the nearby DIY-shop
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  16. #16
    Join Date
    Jan 2004
    Location
    South Africa
    Posts
    71
    Rep Power
    21

    Re: Evasive gas leak

    My experience with ultrasonic leak detectors have been very good.I have pinpointed gas leaks where my electronic leak detector goes crazy due to the over contamination of the leak in confined areas such as piping in tranches and eveporators in cold rooms.
    I use the electronic leak detector to locate the general area of the leak and then zoom in with my ultrasonic leak detector.
    For me it has been a valuable tool.
    Regards,
    Feeze

  17. #17
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Evasive gas leak

    Can't you reset your leakdetector to a new higher concentration level or starting level so that it doesn't take in account the gas in the room?

    What ultrasonic do you use? Perhaps I use it the wrong way.
    My experience with the ultrasonic is that you always must be right on the leak before you can trace it.
    And if you find it then finally, mostly you then even can hear it if it's very quit.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  18. #18
    Join Date
    Jan 2004
    Location
    South Africa
    Posts
    71
    Rep Power
    21

    Re: Evasive gas leak

    Peter_1.
    Yes I have an excellent electronic leak detector which I can reset to the higher surrounding concentration of gas until I find the leak and I have been successful in about 95% of my efforts.
    In the other 5% of the cases other methods are required,
    the soap bubble method-when you know where the leak is and you have good excess to it but you need to know if it is the whole joint or only a small part of the weld,
    the dye method I found works well for leaks at the shaft seal of open drives,
    and the ultrasonic which as I said before worked for me in pipe trenches where the gas concentration is saturated and there are so many pipes that you do not know where to begin looking.
    Also in eveporators in cold/freezer rooms where your electronic leak detector indicates that there is a leak, I find that I am able to zoom in to the offending eveporator (if there is more than 1)
    and probibly the vicinity of the leak but if the leak is in the middle of the eveporator 2 or 3 rows deep, than my ultrasonic detector works best in pinpointing that leak.
    So what I am saying is that I use them together.
    I have an AccuTrak VPE-1000 Made by Superior Signal their top of the line unit.
    My electronic leak detector is a D-Tek all gas unit also their top of the line
    I use Spectrolites ultraviolet kit for the dye method.I found that their big bulb works better than the blue diode flash light from cliplight. However I accidently found out that the blue diode flashlight from cliplight is wonderful for revealing hotspots and arcing in electrical boxes.Try it out and all will be revealed.
    Regards,
    Feeze

  19. #19
    Join Date
    Aug 2004
    Location
    Holland
    Posts
    55
    Rep Power
    20

    Re: Evasive gas leak

    Quote Originally Posted by Temprite
    I use a Javac tek mate.But even though it says for use with r134a.I sometimes have leaks that you can see with soap,but the detector hardly goes off unless you are right on top of the leak with r 134a.Anyone else have this kind of problem?

    Regards.
    I work for a dutch company who is active in the supermarket bussines and we do employ some 80 service engineers (service only).
    We now use the yokogawa H10 pm witch is so sensitive that even a small leak, not vissible using soap can be measured holding the probe in the airoutlet.

    This piece of kit has a 3 level auto sensing setting and when encounterd with big leaks you can switch it to hand ajust with also has 3 settings and a potentiometer to increase or decrease the sensetivity.

    Recently I came among a extreem large leak where even on setting large and totaly turned back it went crazy.

    On the bottom is a other ajustment where you can ajust the temperature of the sensor, by turning this back I could locate the leak wich was in a insulated liquid line above a false ceiling.

    I can tell you that after al lot of leakdetectors passed throug my car this one is by far my favourite.

    Documentation can be found here

    http://firsttechtools.com/yokogawa_h10_pm.htm

    Regards Victor

  20. #20
    Join Date
    Jan 2004
    Location
    South Africa
    Posts
    71
    Rep Power
    21

    Re: Evasive gas leak

    Quote Originally Posted by coolman
    We now use the yokogawa H10 pm witch is so sensitive that even a small leak, not vissible using soap can be measured holding the probe in the airoutlet.

    Recently I came among a extreem large leak where even on setting large and totaly turned back it went crazy.

    Regards Victor
    Which gas Victor?

  21. #21
    Join Date
    Aug 2004
    Location
    Holland
    Posts
    55
    Rep Power
    20

    Re: Evasive gas leak

    Quote Originally Posted by Feeze
    Which gas Victor?
    At this moment the refrigerants we tend tu use are:

    R22
    R134a
    R401a
    R402a
    R404a
    R507

    R404 is the most difficult one to sense, and even very small leaks are found very easely.

    Regards Victor

  22. #22
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Evasive gas leak

    Frank, we use exactly he same powder from Johnson, but last month, we forgot the bottle at home and bought some chalk in the nearby DIY-shop
    Don'tget them mixed up at home Peter - you don't want the kids smelling of chalk after the bath

  23. #23
    Join Date
    Jan 2004
    Location
    South Africa
    Posts
    71
    Rep Power
    21

    Re: Evasive gas leak

    Here is a link to info on leak detection methods
    http://www.bacharach-training.com/methods.htm

    Cheers,
    Feeze

  24. #24
    a/c doctor's Avatar
    a/c doctor Guest

    Re: Evasive gas leak

    The best and sure way to find any leak is to decant system (unless R22) add some R22 and pressure test with OFN.Then get the old butane leak lamp out.
    Never failed me.

    a/c Doctor

  25. #25
    Join Date
    Feb 2007
    Location
    UK
    Age
    58
    Posts
    158
    Rep Power
    18

    Re: Evasive gas leak

    Quote Originally Posted by a/c doctor View Post
    The best and sure way to find any leak is to decant system (unless R22) add some R22 and pressure test with OFN.Then get the old butane leak lamp out.
    Never failed me.

    a/c Doctor
    Shame that method is illegal in UK

    Adding R22 to a leaking system could get you locked up

Similar Threads

  1. Leak detectors
    By Temprite in forum Tools and Calculators
    Replies: 54
    Last Post: 18-08-2010, 04:15 PM
  2. Tiff 5000 leak detector
    By davidchesson in forum Tools and Calculators
    Replies: 6
    Last Post: 06-11-2006, 05:26 AM
  3. Can't find leak with UV Dye
    By jd_boggs in forum Transport
    Replies: 6
    Last Post: 16-09-2006, 06:22 PM
  4. oil leak
    By bernard in forum Supermarket Refrigeration
    Replies: 8
    Last Post: 05-09-2004, 06:01 PM
  5. Annual Leak Test
    By Dave Finlay in forum Air Conditioning
    Replies: 9
    Last Post: 04-04-2004, 12:35 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •