Results 1 to 16 of 16
    Mar 2010
    7
    Heat Pump Component Design Efficiency
    I am interested in the inherent efficiency and performance limitations of various Heat Pump components.
    I'll start a sub thread for specific components.
    rimmer
    Mar 2010
    7
    Re: Heat Pump Component Design Efficiency: Expansion Valves
    Do you know of any specific losses or efficiency issues associated with current heat pump expansion valves? Are friction losses noticeable?
    Aug 2009
    New Zealand
    2,554
    26
    An expansion valve, is device that restricts flow, so by definiation, friction is noticable.
    Mar 2010
    7
    Are there any figures quoted for this friction loss in a vapour compression heat pump?
    Any other efficiency issues, say, due to loss of suction?
    Aug 2009
    New Zealand
    2,554
    26
    Quote Originally Posted by rimmer View Post
    A heat pump in principle is no different to refrigeration, a huge amount info is available on refrigeration principles, start with the basics. You have to master this before you starting looking into specifics.
    Mar 2010
    7
    Quote Originally Posted by mad fridgie View Post
    I'm familiar with the basic principles: I'm trying to understand the various causes of energy loss through out the system. Some causes are better documented than others.
    rimmer
    Aug 2009
    New Zealand
    2,554
    26
    rimmer
    being familar is not quite the same as master the basic principles. If you master them , you will find that most of your answers to your future questions, become apparent.
    So lets have a look at the suction line ( a question asked) I will ask you questions to aid better understanding (general applications)
    Is it hot or cold?
    Is energy absorbed or rejected? (is this useful or not?)
    Whats happens to the pressure down the length?
    What effect do the above have on density.
    Does this have an inffluence on the compressor?, if yes/no why?
    11,025
    Means compressor is broken, somewhat inefficient.
    Mar 2009
    KZN, South Africa
    63
    2,212
    As MF mentoned, by their very nature, they should be. If not, then I'd begin looking for a new TXV supplier.
    Mar 2009
    KZN, South Africa
    63
    2,212
    @rimmer:
    Perhaps you could start by telling us more about yourself, & your interest in heat-pumps?
    Aug 2009
    New Zealand
    2,554
    26
    Well I missed that one!!!! LOL
    Mar 2010
    7
    I am an MSc student writing a paper on user control of heat pumps.
    As part of my context, I am describing theoretical limits to COP due to Carnot and the P-H characteristics of the refrigerant. I am also looking at mechanical and electrical losses as well as system inefficiencies due to intermittent control.
    This post is trying to pick up on some of the 'in the field' knowledge that you HVAC guys may have in this area.
    rimmer
    Aug 2009
    New Zealand
    2,554
    26
    rimmer
    I will point you in a direction, look at electrical energy in, not KWs but KVA (power factor) this has a large influence on power supply systems, this is specific to components.
    I presume you are talking air to air heat pumps, you then need to look what comfort levels effecting (Ie hot or cold start for fans)
    Then you need to look at location of equipment and effects of stratification in relation to comfort level (cold feet syndrome)
    Mar 2010
    7
    No, Not air source. Ground or Water Source
    Mar 2010
    7
    ...... and hydronic underfloor heating. However, the build environment and thermal comfort is not the subject of this post
    Aug 2009
    New Zealand
    2,554
    26
    Is thermal comfort the goal, so then has to be the starting point, if not then, any theory is flawed. This must affect the intermittent, control. Is this not what you are asking?
    Are you not in effect trying to balance losses verses gains during a cycling system (energy mass balance)
    the carnot cycle is well proven, so not quite sure what you are trying achieve.
    maybe you can ask specific questions.
  1. Design heat pump for a pool
    By rolandh in forum Heat Pumps
    Last Post: 23-09-2010, 10:50 AM
  2. Heat Pump Design
    By behmin in forum Heat Pumps
    Last Post: 22-03-2009, 09:00 PM
  3. electromagnetic defrost heat pump?
    By star882 in forum New Technologies
    Last Post: 08-03-2007, 10:09 AM
  4. Rebuild air2air heat pump
    By stalker in forum Technical Speculations
    Last Post: 02-11-2006, 10:10 AM
  5. R134a <-> liquid heat exchanger design
    Last Post: 10-05-2002, 08:36 AM