Results 1 to 18 of 18
    simon sheppard's Avatar
    simon sheppard Guest
    P trap correct installation
    Im currently installing some large DX comms room units.
    I have a riser lift of about 8m to 10m, and have been specified to install p traps and oil traps for the remote condenser pipe work.
    Can any one specify the correct way of performing this, as several ways have been brought to my attention.
    Basically i have a 8 to 10m riser and i would like to know whether i put traps on both discharge and liquid? p traps at the bottom and oil traps half way up??
    people are confusing me on the correct way?????
    would appreciate some ones advice??
    thank you
    11,025
    Re: P trap correct installation
    If you want to get really technical have a look at this pipe guide from McQuay, PDF
    http://www.mcquay.com/mcquaybiz/lite...011_120407.pdf
    Dec 2008
    564
    Great information Brian, thanks.
    Sep 2003
    ISRAEL
    72
    4,248
    Thanks Brian for a useful link.
    I saw somewhere[cant remember where], from the bottom of the U trap, 3\8 tube going up to the top of the riser. For my my question how does that help, i was answered that the pressure in the small tube is a bit higher then the large suction pipe and it takes the oil much better up.
    Of course a good oil separator is required.
    Dec 2008
    Isle of Man
    55
    42
    I was told by Emerson for a similar job; traps on discharge pipework at bottom of all rises and 6M intervals.
    For example, the system i installed was thus; the pipework ran under computer floor and then up the internal wall for 2M (TRAP INSTALLED AT BOTTOM), pipework exited through wall and ran laterally along wall for 12M where it then ran up the wall (TRAP INSTALLED AT BOTTOM). There was then a rise of 10M to roof level (TRAP INSTALLED 6M FROM BOTTOM).
    Croatia
    68
    2,261
    Hi, simon sheppard
    check this link ... maybe you can find some good info for you....
    http://www.refrigeration-engineer.co...ead.php?t=4392
    also, searching RE forums maybe you can find more information ...
    Best regards, Josip
    Split Croatia
    6,151
    While we are at traps, what would be better, trap made of fittings with smallest dimensions as possible like with 2 45° and one 90° elbow or trap made with bending tools with required minimum bending radius? And what are aceptable dimensions?
    Is it same for normal and inverted trap at top of riser?
    11,025
    I would have thought that a pulled bend would be better due to the reduction in pressure drop.
    Feb 2010
    cape town
    9
    Quote Originally Posted by chemi-cool View Post
    Hi Simon I also read in a Trane Manual excerpt where they pointed out that when using unloading compressors you use this double riser system on the discharge line .The larger pipe goes up to the top of the hot gas line through an inverted trap; so that during the low load conditions the oil in this larger riser will not enter into the smaller riser which will be solely carrying the gas flow. I hope this helps !
    Split Croatia
    6,151
    Feb 2010
    cape town
    9
    .....oooh I see thanks for the correction Nike123
    Split Croatia
    6,151
    Quote Originally Posted by rk tigere View Post
    It was misunderstanding from my part!
    But smaller riser will not carry only gas. It will still carry oil with refrigerant and with sufficient speed at low load condition because trapped oil in P trap act as plug in bigger pipe.
    Problem with this is that if it is lot of P traps (and they are not small as possible), high amount of oil is trapped in these P traps during low load condition (and not returning in compressor).
    http://books.google.hr/books?id=gniJ...0riser&f=false
    Split Croatia
    6,151
    I don't see how pressure in small pipe cold be higher with "connected vessels" (what is correct term?) law in mind.
    Only capillary action comes to my mind.
    Split Croatia
    6,151
    I have read somewhere, that with arrangement like this:
    oil in trap is better mixed and carried with refrigerant because of turbulence in sudden change in direction with 90° short radius elbow.
    Pressure drop could be compensated with bigger lines diameter at horizontal lines.
    Also, that way oil in trap is minimal as much as it could be (and cannot be "minimalier") as oppose to this arrangement:
    Also, I would like to know equivalent length of standard P traps.
    Split Croatia
    6,151
    Here is what I found on that subject:
    11,025
    Good set of images, thanks.
    Croatia
    68
    2,261
    Hi, nike123
    really good one, thanks for efforts,
    waiting now for original poster
    Best regards, Josip
    Sep 2003
    ISRAEL
    72
    4,248
    Good info Nike, I will give it a try on my next installation.
    Too bad copper is not transparent, I would like to see how it works inside.
  1. The correct way to write CO2.
    By nic_f in forum CO2
    Last Post: 09-02-2009, 07:27 PM
  2. Installation of NRVS check valves
    By Josip in forum NH3
    Last Post: 02-12-2008, 01:33 PM
  3. Q: Piping installation for Split Types
    By brianubaldo in forum Refrigerants
    Last Post: 30-04-2008, 02:23 PM
  4. Replies: 5
    Last Post: 11-07-2007, 03:06 AM
  5. Evaporative condenserīs liquid drain trap
    By Volnei in forum Industrial
    Last Post: 24-10-2003, 02:46 AM