    P trap correct installation



    Hi,

    Im currently installing some large DX comms room units.

    I have a riser lift of about 8m to 10m, and have been specified to install p traps and oil traps for the remote condenser pipe work.

    Can any one specify the correct way of performing this, as several ways have been brought to my attention.

    Basically i have a 8 to 10m riser and i would like to know whether i put traps on both discharge and liquid? p traps at the bottom and oil traps half way up??

    people are confusing me on the correct way?????


    would appreciate some ones advice??


    thank you



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: P trap correct installation

    If you want to get really technical have a look at this pipe guide from McQuay, PDF

    http://www.mcquay.com/mcquaybiz/lite...011_120407.pdf
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Dec 2008
    Location
    UK
    Posts
    568
    Rep Power
    24

    Re: P trap correct installation

    Great information Brian, thanks.

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: P trap correct installation

    Thanks Brian for a useful link.

    I saw somewhere[cant remember where], from the bottom of the U trap, 3\8 tube going up to the top of the riser. For my my question how does that help, i was answered that the pressure in the small tube is a bit higher then the large suction pipe and it takes the oil much better up.

    Of course a good oil separator is required.

  5. #5
    Join Date
    Dec 2008
    Location
    Isle of Man
    Age
    55
    Posts
    42
    Rep Power
    0

    Re: P trap correct installation

    I was told by Emerson for a similar job; traps on discharge pipework at bottom of all rises and 6M intervals.
    For example, the system i installed was thus; the pipework ran under computer floor and then up the internal wall for 2M (TRAP INSTALLED AT BOTTOM), pipework exited through wall and ran laterally along wall for 12M where it then ran up the wall (TRAP INSTALLED AT BOTTOM). There was then a rise of 10M to roof level (TRAP INSTALLED 6M FROM BOTTOM).

  6. #6
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: P trap correct installation

    Hi, simon sheppard

    check this link ... maybe you can find some good info for you....

    http://www.refrigeration-engineer.co...ead.php?t=4392

    also, searching RE forums maybe you can find more information ...


    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: P trap correct installation

    While we are at traps, what would be better, trap made of fittings with smallest dimensions as possible like with 2 45° and one 90° elbow or trap made with bending tools with required minimum bending radius? And what are aceptable dimensions?
    Is it same for normal and inverted trap at top of riser?

  8. #8
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: P trap correct installation

    I would have thought that a pulled bend would be better due to the reduction in pressure drop.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  9. #9
    Join Date
    Feb 2010
    Location
    cape town
    Posts
    9
    Rep Power
    0

    Re: P trap correct installation

    Quote Originally Posted by chemi-cool View Post
    Thanks Brian for a useful link.

    I saw somewhere[cant remember where], from the bottom of the U trap, 3\8 tube going up to the top of the riser. For my my question how does that help, i was answered that the pressure in the small tube is a bit higher then the large suction pipe and it takes the oil much better up.

    Of course a good oil separator is required.
    Hi Simon I also read in a Trane Manual excerpt where they pointed out that when using unloading compressors you use this double riser system on the discharge line .The larger pipe goes up to the top of the hot gas line through an inverted trap; so that during the low load conditions the oil in this larger riser will not enter into the smaller riser which will be solely carrying the gas flow. I hope this helps !

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: P trap correct installation

    ..............................
    Last edited by nike123; 11-03-2010 at 10:04 AM.

  11. #11
    Join Date
    Feb 2010
    Location
    cape town
    Posts
    9
    Rep Power
    0

    Re: P trap correct installation

    .....oooh I see thanks for the correction Nike123

  12. #12
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: P trap correct installation

    Quote Originally Posted by rk tigere View Post
    .....oooh I see thanks for the correction Nike123
    It was misunderstanding from my part!

    But smaller riser will not carry only gas. It will still carry oil with refrigerant and with sufficient speed at low load condition because trapped oil in P trap act as plug in bigger pipe.
    Problem with this is that if it is lot of P traps (and they are not small as possible), high amount of oil is trapped in these P traps during low load condition (and not returning in compressor).

    http://books.google.hr/books?id=gniJ...0riser&f=false
    Last edited by nike123; 11-03-2010 at 04:30 PM.

  13. #13
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: P trap correct installation

    Quote Originally Posted by chemi-cool View Post
    Thanks Brian for a useful link.

    I saw somewhere[cant remember where], from the bottom of the U trap, 3\8 tube going up to the top of the riser. For my my question how does that help, i was answered that the pressure in the small tube is a bit higher then the large suction pipe and it takes the oil much better up.

    Of course a good oil separator is required.
    I don't see how pressure in small pipe cold be higher with "connected vessels" (what is correct term?) law in mind.
    Only capillary action comes to my mind.
    Last edited by nike123; 11-03-2010 at 11:37 AM.

  14. #14
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: P trap correct installation

    Quote Originally Posted by Brian_UK View Post
    I would have thought that a pulled bend would be better due to the reduction in pressure drop.
    I have read somewhere, that with arrangement like this:



    oil in trap is better mixed and carried with refrigerant because of turbulence in sudden change in direction with 90° short radius elbow.
    Pressure drop could be compensated with bigger lines diameter at horizontal lines.
    Also, that way oil in trap is minimal as much as it could be (and cannot be "minimalier") as oppose to this arrangement:


    Also, I would like to know equivalent length of standard P traps.
    Last edited by nike123; 11-03-2010 at 04:26 PM.

  15. #15
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: P trap correct installation

    Here is what I found on that subject:








  16. #16
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: P trap correct installation

    Good set of images, thanks.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  17. #17
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: P trap correct installation

    Hi, nike123

    really good one, thanks for efforts,

    waiting now for original poster

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  18. #18
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: P trap correct installation

    Good info Nike, I will give it a try on my next installation.

    Too bad copper is not transparent, I would like to see how it works inside.

Similar Threads

  1. The correct way to write CO2.
    By nic_f in forum CO2
    Replies: 5
    Last Post: 09-02-2009, 08:27 PM
  2. Installation of NRVS check valves
    By Josip in forum NH3
    Replies: 10
    Last Post: 02-12-2008, 02:33 PM
  3. Q: Piping installation for Split Types
    By brianubaldo in forum Refrigerants
    Replies: 11
    Last Post: 30-04-2008, 02:23 PM
  4. Replies: 5
    Last Post: 11-07-2007, 03:06 AM
  5. Evaporative condenserīs liquid drain trap
    By Volnei in forum Industrial
    Replies: 7
    Last Post: 24-10-2003, 02:46 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •