    I am looking to choose between 2 ice block plants. One is rated at 15.2A and the other is 38.2A.
    Voltage will be 380-400v/3/50hz.

    I want to get a generator that will be sufficient in running them (separately) cos i will be choosing either of them.

    How do i choose the right sized generator?. (Not too big nor too small)

    Thanks



  2. #2
    Join Date
    May 2006
    Location
    Serbia
    Age
    60
    Posts
    13
    Rep Power
    0

    Re: What Size Generator/Amps Do i Need for my Ice Block Plant

    If cos fi ice plant is 0.85, then 38.2A plus looses in motors, about 7A, total generator need about 45.2A min.
    Did you calculate total consuption ice plant, eg. water blower, pumps for recirkulation ice water...
    Inductive consumer is highli demand on start, so total power of the generator probably will be increase *1.7!

Similar Threads

  1. Replies: 14
    Last Post: 05-01-2011, 12:12 AM
  2. Block Ice Plant Operation
    By 4xfoot in forum Industrial
    Replies: 0
    Last Post: 05-02-2010, 10:50 AM
  3. ICE block plant
    By uma maheswar in forum Technical Discussions
    Replies: 0
    Last Post: 06-12-2009, 03:23 AM
  4. Fujitsu Window unit Size 9 same size as 6 ?
    By S_Line in forum Air Conditioning
    Replies: 1
    Last Post: 19-09-2008, 01:05 PM
  5. Used Ice Block Plant
    By apilorge in forum Industrial
    Replies: 1
    Last Post: 10-04-2008, 12:19 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •