    ICAD 900 problems



    good day to you all

    where having some problems using a icad 900 with a icm65
    \we use it for defrosting our plate freezers on board an dutch frezing trawler
    now the problem we are have is
    it seem the valve is not opening quickly
    when we give the valve some pre opening its going oke for several times
    then over a period of time (approx 1 hour)
    The pre opening is disserpearing
    and the valve or icad seem to be to late to open again

    we trided re callibrating
    checked all the setting
    everyting seem to be in order
    after recalibration the vale works fine by th way
    but after approx 1 hour the malfuntion begins again

    the valve is in a co2 system

    hope somone can help me

    berst regards jack eelman



  2. #2
    Join Date
    Nov 2009
    Location
    france
    Age
    64
    Posts
    226
    Rep Power
    19

    Re: ICAD 900 problems

    Your problem is that some moisture, when it's frosted, is locking the actuator to rotor sleeve. you should remove the actuator, warm and dry the sleeve and apply greeze with a deep freezing point. it will prevent moisture to get in.

  3. #3
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: ICAD 900 problems

    Danfoss recommend gland heater be installed on ICAD for any application minus 30 C & lower .

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: ICAD 900 problems

    Cricri has pin pointed the logical cause and Ranger's advice is spot on!
    We even fit them on chill applications.
    Well worth acting upon both recommendations.
    Grizzly.

  5. #5
    Join Date
    Nov 2009
    Location
    france
    Age
    64
    Posts
    226
    Rep Power
    19

    Re: ICAD 900 problems

    Hello,

    I'am back to my office, you 'll find some quote of an instruction delivered with a new ICAD900
    Attached Files Attached Files

Similar Threads

  1. Oil problems with a dual temperature pack.
    By Chunk in forum Supermarket Refrigeration
    Replies: 33
    Last Post: 11-09-2008, 03:29 AM
  2. Problems LG don't want you to know about
    By Andy W in forum Air Conditioning
    Replies: 11
    Last Post: 16-02-2006, 05:52 PM
  3. Oil return problems
    By Peter_1 in forum Industrial
    Replies: 37
    Last Post: 23-08-2004, 11:30 PM
  4. oil pressure problems on air dryer
    By edge in forum Trouble Shooting
    Replies: 1
    Last Post: 16-07-2002, 02:10 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •