    good day to you all
    where having some problems using a icad 900 with a icm65
    \we use it for defrosting our plate freezers on board an dutch frezing trawler
    now the problem we are have is
    it seem the valve is not opening quickly
    when we give the valve some pre opening its going oke for several times
    then over a period of time (approx 1 hour)
    The pre opening is disserpearing
    and the valve or icad seem to be to late to open again
    we trided re callibrating
    checked all the setting
    everyting seem to be in order
    after recalibration the vale works fine by th way
    but after approx 1 hour the malfuntion begins again
    the valve is in a co2 system
    hope somone can help me
    berst regards jack eelman
    Nov 2009
    france
    58
    139
    12
    Re: ICAD 900 problems
    Your problem is that some moisture, when it's frosted, is locking the actuator to rotor sleeve. you should remove the actuator, warm and dry the sleeve and apply greeze with a deep freezing point. it will prevent moisture to get in.
    2,609
    29
    Danfoss recommend gland heater be installed on ICAD for any application minus 30 C & lower .
    Somerset
    64
    4,596
    40
    Cricri has pin pointed the logical cause and Ranger's advice is spot on!
    We even fit them on chill applications.
    Well worth acting upon both recommendations.
    Grizzly.
    Nov 2009
    france
    58
    139
    12
    Hello,
    I'am back to my office, you 'll find some quote of an instruction delivered with a new ICAD900
    Attached Files Attached Files
  1. Oil problems with a dual temperature pack.
    By Chunk in forum Supermarket Refrigeration
    Last Post: 11-09-2008, 03:29 AM
  2. Problems LG don't want you to know about
    By Andy W in forum Air Conditioning
    Last Post: 16-02-2006, 04:52 PM
  3. Oil return problems
    By Peter_1 in forum Industrial
    Last Post: 23-08-2004, 11:30 PM
  4. oil pressure problems on air dryer
    By edge in forum Trouble Shooting
    Last Post: 16-07-2002, 02:10 PM