Results 1 to 50 of 224
Thread: Strange TXV setup
06-03-2010, 04:18 AM #1
Strange TXV setup
There have been several recent threads that have made me think about this setup in a new light.
The system has 3 boxes each with holdover plates, the refrigerant passes through each one in turn and running temps in each box are:-
Freezer -10 to -12C (2 plates at -20C)
Refrigerator 2 to 4C (plate -6C)
Salad Chiller 4 to 8C (plate -4C)
But the TXV is inside the freezer and the bulb is inside the Chiller so once the system's down to temps one must assume that the TXV will be sensing the diaphragm temperature and not the bulb's at some instant. Maybe as the system cools down further on cycle the bulb see temps lower than than the freezer?
However, it works, but is very susceptible to charge.
I've already got the message that it may be better to get the TXV say into the chiller but why does it work as it is? Any ideas
Chef
Oh - its R134 and running Dx = 125PSI and Sx = 2PSI
06-03-2010, 05:29 AM #2
Re: Strange TXV setup
You are indicating that the evaps plates are in series?
You have single TXV and the bulb is on the outlet of salad evap, you have the superheat set very high?
06-03-2010, 05:35 AM #3
I'm thinking there must be more to the story, some means of controlling the temps of the warmer plates.
06-03-2010, 06:00 AM #4
MF - the plates are indeed in series with with one TXV and the bulb is on the outlet pipe of the chiller but I cant really determine the SH as it may be the diaphragm thats trying to control it?
Gary - There is no temperature control of any plate but it is a holding system so it is run for about 1 hour and all the plates freeze, each one has a different ratio of ethylene glycol so it freezes at a different temp and the plates get smaller relative to the box size as the box temps are higher. It is a manual timer and switched on when the system looks like it needs some more cold - say 60 mins in the morning and 30 mins at night.
Chef
06-03-2010, 06:35 AM #5
06-03-2010, 06:46 AM #6
Internal equaliser - TF2 with #4
The simple diagram shows the basic layout but the desuper, condenser, accumulator, dryer, sight glass not shown.
The liquid line to suction exchanger is inside the chiller but the bulb is between it and the chiller plate
Chef
06-03-2010, 07:01 AM #7
Interesting. If we assume the charge has migrated, then the TXV should be at minimum flow.
06-03-2010, 07:23 AM #8
06-03-2010, 07:28 AM #9
06-03-2010, 07:41 AM #10
06-03-2010, 08:00 AM #11
06-03-2010, 07:25 AM #12
But there is the rub, the system sucks itself down like a big dog.
If the freezer is at say -6 at startup around the diaphragm (as it is at the top of the freezer) and the suction goes down to 2 to 4 PSI the valve should open but there is a large pressure drop through the system, there is pressure tap just after the TXV and one on the compressor but I cant find the data that I measured a while ago - seem to remember about 8PSI.
Also the TXV is set to a very low SH to get best performance. Seems like it may be working somehow from the diaphragm temp alone?
I am just trying to think out loud here, what if the diaphragm stays roughly constant and the valve meters the refrigerant through pressure drop changes in the evap? As the flow rate increase the pressure increase and so closes the valve a little
Never heard of a TXV working like that before though?
Chef
06-03-2010, 07:28 AM #13
Just a silly question first "Accumulator"
for clarity is a suction accumulator,
do you have a liquid reciever?
What do you mean" but is very susceptible to charge."
As gary asked internal or external equalised?
06-03-2010, 07:35 AM #14
Your right it is a receiver and not an accumulator, there is no suction accumulator.
The receiver is also quite small - the type you find on a car A/C system.
The system seems to work more like a cap tube system or orifice system in that a few puffs of gas can move the frost line along the liquid/suction exchanger and vise versa. So when the system is settled in and cycling we check the exchanger and add a little gas to optimise its pull down times.
Internal equalisation.
Chef
06-03-2010, 07:45 AM #15
If in doubt go external equalised (what is your evap design pressure drop) This can cause hunting of the valve and prematurely close the valve!
I suspect that there is no or little work being done in freezer plates.
Comp SST -22C, plates -20C, it is likely that liquid is just sitting in the evap, (like a capillary).
TEV not a problem!
06-03-2010, 08:16 AM #16
External equalised might make it worse because of the TXV's position in the freezer.
The freezer plates get cold and stay cold so we have to assume they are working fine.
So here is a what if idea.
What if the system is critically charged and the freezer takes the lion share of cold, then the fridge and chiller take a little but are more responsible for the systems SH (the gas will still be nicely cold enough to cool these smaller plates) and the temp going to the compressor is about 10 or 15C - its not frosted out of the boxes!!
Chef
06-03-2010, 08:24 AM #17
Sorry you mis-understand, when your plates are frozen there is no load to boil the refrigerant (only flow is flash gas, with a little liquid carry over, mass of refirgerant is being held in the freezer plates, if you increase your reciever size (thus charge) then liquid could flow correctly to next plates, then valve would control on superheat.
At the moment you are critical charge.
06-03-2010, 08:45 AM #18
I get the point about the freezer plates being the controlling part and the suction would drop quickly if we did not turn it off, but the whole point seems to be diaphragm is stuck in the freezer and so the bulb will never get used in the control.
I know I will have to move the TXV to another location to make it work and as you say get a bigger receiver.
Or maybe just leave it as it is and continue to do manual control? Nah - too much of a challenge really.
Chef
06-03-2010, 08:51 AM #19
09-03-2010, 05:30 AM #20
06-03-2010, 08:01 AM #21
Being internally equalized the saturation temp sensed by the TXV is that of the freezer evap. Assuming migrated charge, the TXV is maintaining a difference between freezer evap saturation and freezer air temp, both of which would change very slowly... giving you a fixed flow, very much like a fixed orifice.
06-03-2010, 08:34 AM #22
This seems to be the only conclusion but how strange is this phenomena. The setup must be just so coincidentally right that it appears the TXV does something.
If one adjusts the SH on the TXV the suction pressure changes so one assumes the valve is functioning as a TXV but in fact it may be just changing the size of the orifice.
Now thats quite interesting.
So what is the best solution out of this problem. Although I call it a problem but it has worked faultlessly for many years and now its seems not be what it should be ie a TXV controlled system it would be nice to set it right.
Chef
06-03-2010, 08:05 AM #23
Apparently the various glycol solutions determine the different box temps.
06-03-2010, 08:15 AM #24
Changing to external equalized without changing the TXV location would be interpreted as higher superheat causing higher refrigerant flow, but the flow would still be fixed... albeit at a higher rate. You would need to remove some refrigerant.
06-03-2010, 08:41 AM #25
I suspect the different glycol mixtures are what makes it all work regardless.
Moving the TXV and going with external equalizer would freeze the plates faster and more closely control the SH returning to the compressor... and the charge would no longer be critical.
06-03-2010, 09:06 AM #26
Well, controlling the SH might be a good idea as compressor failures are a bi-annual event probably due to poor suction conditions.
However changing anything is a nightmare in space and a mix of swagelok, brazed, SAE and hydraulic hose fittings makes it a headache. I will have to do some major surgery. Its an inherited system.
Chef
PS I bet it would be very difficult to design a system with the correct glycol concentrations and a TXV acting as an orifice from scratch to work!!!!
06-03-2010, 03:53 PM #27
07-03-2010, 01:24 AM #28
The working faultlessly bit is the fact that it cools everything down and has appeared to working as a TXV controlled system, now we know that is not the case.
For many years it has done what it is supposed to but the compressors fail every 2 or 3 years.
We had always assumed this was because the unit is a car A/C compressor designed for air con duty and not LBP freezer work so it gets pushed quite hard. Now with this new info it makes me wonder if the 'orifice' system could help in the failures. Haven't figured that out yet.
The Sx would be about the same with a TXV and an orifice.
With the orifice the boxes get a gradient of cooling that seems to be just right but with a TXV they will all get sucked down -20C in each plate, that may present a new problem.
Chef
07-03-2010, 05:06 AM #29
06-03-2010, 08:44 AM #30
On the other hand, it seems to be working fairly well as a fixed orifice system.
06-03-2010, 08:56 AM #31
From a pure RD perspective, you should only make one change at a time.
If you think you need a bigger reciever, do this first, recharge then test.
This method you can prove 100% where changes happen, if you try all together, I am sure everything would be sorted, but will only guess what you have fixed. human natures says what you think must be true!
06-03-2010, 09:14 AM #32
06-03-2010, 09:27 AM #33
06-03-2010, 04:18 PM #34
07-03-2010, 06:53 AM #35
What happens to the compressor, does it seize?
07-03-2010, 07:04 AM #36
Not always - we only had one seize and that made a mess but others just get really noisy and when it sounds 'ripe to be picked' we replace it. Oil is correct quantity in the compressor and clean so can only assume severe duty. We hear other people also have the same problem running these AC compressors as freezer units.
The reason to use them is they are cheap, buy them anywhere, very compact and light and really powerful - all good signs of premature failure I suppose.
Chef
07-03-2010, 08:09 AM #37
Move TXV bulb to freezer suction, insider the freezer cabinet. Problem one sorted, (run low superheat 2-3C)
Install 2 comps in series (2 stage), lower speed of each compressor.
Bigger reciever
07-03-2010, 08:30 AM #38
I will have to think about the bulb in the freezer, it may work and its a good idea. Interesting idea as the rest of the system is still on SH cooling.
2 compressors - easier to just replace them every 2 years or so but if I lower the speed of the compressors the flow rate will fall - more problems here I see, lower gas velocity, oil return poor performance etc.
Bigger receiver I got that already, but only if I can get the TXV to work like a TXV - maybe your bulb idea has merit. Think upon this I will.
Chef
07-03-2010, 08:36 AM #39
07-03-2010, 08:54 AM #40
If the compressors are in series they must run at he same RPM to get the same flow rate but they will have half the pressure ratio.
If the compressors are in parallel then they will need to be run at half speed and and they will still have the same high pressure ratio.
Its a thought but not sure its the best solution.
Chef
07-03-2010, 09:09 AM #41
Car AC comp have avery short piston stroke (especially swash plate), so pressure difference becomes very important as far as volumetric efficiency.
There is a gap between the piston and the discharge valve, this is filled with compressed gas, on the down stroke (suction) no gas is drawn in until the higher pressure gas expands to meet the suction pressure.
So you actual mass flow through the compressor is likely to be quite low. Low volumetric efficiency.
Going 2 stage, reduces the the pressure drop, increasing volumetric efficiency, thus increasing actual mass flow. So slowing the speed down will bring actual mass flow back to original amount. Slower speed less mechanical stress, lower discharge temps.Increased life!!! and is actually more efficient as far as power goes.
(forgot to say interstage does need cooling)
07-03-2010, 08:41 AM #42
Moving the bulb to the freezer would solve the charge migration problem.
Then we would see if the other plates are indeed SH cooled.
07-03-2010, 09:04 AM #43
07-03-2010, 09:14 AM #44
07-03-2010, 09:08 AM #45
Nice representation.
07-03-2010, 09:28 AM #46
07-03-2010, 09:17 AM #47
SH cooling is not new, the term we use is "useful superheat" verses non useful superheat (heat absorbed say down the suction line, and can also can be expressed as suction line pressure drop)
07-03-2010, 09:17 AM #48
MF - I understand the prblems with the swash plate compressors and the volumetric efficiency thats why thet fail a lot but if you run slower then the volumtric flowrate will drop.
These units are are 140cc per rev so if we slow it down it will be less volume and less mass flow.
The pair of compressors must run at the same speed!
Well actually the first one must run at the same speed and the second one must be smaller and designed to run with the output of the 1st compressor - seems quite tricky but solvable.
ChefLast edited by Chef; 07-03-2010 at 09:36 AM. Reason: For correctness
07-03-2010, 09:30 AM #49
07-03-2010, 09:56 AM #50
OK if the volumetric efficiency improves because of the lower pressure ratio the compressor can be run slower by the ratio of the efficiencies at the 2 pressure ratios.
It may be at best 20 %. (probably more like 5%)
So I agree it will go a bit slower. But the second compressor will now be getting gas a higher pressure and so the volume will be lower and it will need to be a smaller compressor. If the first compressor is 140cc per rev the second might be around 50cc per rev. The problem here is there are not many AC car units of this
size? In fact I do not know of any?
Double stage compression with inter cooling is a fascinating subject but I am not sure its right for this application - yet.
Chef
size
Can't suss strange paramaters on Denco downflow unit
By Coolie in forum Air ConditioningReplies: 20Last Post: 26-07-2010, 03:20 PM -
The Basic Setup
By ice_cold in forum FundamentalsReplies: 5Last Post: 17-12-2009, 09:34 AM -
Fujitsu strange Whistling noise
By gwilliamson in forum Air ConditioningReplies: 17Last Post: 26-03-2008, 09:48 PM -
Hermetic strange sound.
By fridg in forum Technical SpeculationsReplies: 16Last Post: 02-03-2008, 07:08 PM -
strange inverter problem
By rbartlett in forum Air ConditioningReplies: 11Last Post: 19-05-2006, 08:31 PM