    Hi all,

    I am still very new to the trade and still have alot to learn.

    I am just after a bit of advice.

    I replaced a compressor the other day on a heat pump unit, the system is on R22 and requires a charge of 5.44kg.

    I decided to way the charge in as its a package unit, I trickle charged it into the suction as a liquid not exceeding 2.5 bar.

    I noticed the compressor was getting very hot although the the suction was nicely frosted. As though it wasnt getting enough cooling from the charge in. and then it went out on thermal.

    Now fully charged the system seems to be running fine and am getting all the corrrect temps/pressures.

    Could this of been down to the change over valve in the wrong position. Ie not in cooling mode???

    Thanks in advance for any advice given.



  2. #2
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: What was I doing wrong

    I trickle charged it into the suction as a liquid not exceeding 2.5 bar.

    I noticed the compressor was getting very hot although the the suction was nicely frosted. As though it wasnt getting enough cooling from the charge in. and then it went out on thermal.
    I feel a little sorry for the poor compressor.

    Why did you not vapour charge into the suction line of an operating system?
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  3. #3
    Join Date
    Mar 2009
    Location
    Mancheser
    Age
    41
    Posts
    55
    Rep Power
    16

    Re: What was I doing wrong

    I have just been used to doing it this way from charging zeotropes.

    Charging at such a low pressure will cause it to boil off into the manifold/sytem before it reaches the compressor would it not?

  4. #4
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: What was I doing wrong

    Point taken. Would it not have been better to charge into the liquid line - as liquid - with the system offline?

    There are adapters which can be used to ensure that the liquid has really & truly vapourised, if you are going to charge that way.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  5. #5
    Join Date
    Mar 2009
    Location
    Mancheser
    Age
    41
    Posts
    55
    Rep Power
    16

    Re: What was I doing wrong

    O right I havent heard of these, what are these called?

    O and I always charge first as a liquid into the liquid line until the pressures equalise. But in this case it took about 50 grams as the ambient was about 4 degrees c.

  6. #6
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: What was I doing wrong

    I think that it might have taken too long for the refrigerant to go in and the compressor overheated in the process, your gauges will only tell you whats in the line and not what the compressor is seeing when charging like that.

    When the weather is cold it can be helpfull to warm the bottle with some warm water in a bucket or a special heater blanket and then dump as much liquid in before you run it.
    Last edited by monkey spanners; 05-03-2010 at 02:45 PM.

  7. #7
    Join Date
    Dec 2008
    Location
    UK
    Posts
    564
    Rep Power
    24

    Re: What was I doing wrong

    In cold conditions, you could with care, use your reclaim pump to pump most of the weight of the liquid into the liquid line before turning the unit on. The remaining trim charge could then be carefully added as vapour once the unit is running.

  8. #8
    Join Date
    Mar 2009
    Location
    Mancheser
    Age
    41
    Posts
    55
    Rep Power
    16

    Re: What was I doing wrong

    Cheers Guys,

    Advice appreciated

    I will try using my reclaimer next time I think.

  9. #9
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: What was I doing wrong

    dont recovery units require lubrication?
    mmm to beer or not to beer...........lets drink breakfast

  10. #10
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    239
    Rep Power
    19

    Re: What was I doing wrong

    was it reclaimed r22 you where using

  11. #11
    Join Date
    Oct 2007
    Location
    Britain
    Posts
    220
    Rep Power
    17

    Re: What was I doing wrong

    You can normally find a warm place to put the refrigerant cylinder before you commence the repairs, will save you loads of time.

    Cheers
    Tutto il Mondo e un Paese

  12. #12
    Join Date
    Mar 2009
    Location
    Jersey
    Posts
    6
    Rep Power
    0

    Re: What was I doing wrong

    Only 50 grams of liquid at 4 degrees r u sure you pulled a good vac on the system ?

  13. #13
    Join Date
    May 2005
    Location
    manchester
    Age
    49
    Posts
    48
    Rep Power
    0

    Re: What was I doing wrong

    always ensure you pull a good vac
    as previously mensioned warm the bottle tub of hot water you can also get heater jackets.
    you can also charge liquid does your manifold have a sight glass?
    if so you can liquid charge very carefully flashing off through your manifold that can be a faster method also

  14. #14
    Join Date
    Jan 2010
    Location
    australia
    Age
    39
    Posts
    32
    Rep Power
    0

    Re: What was I doing wrong

    yes to everything frosty74 has written with your ambient conditions if good vaccum is achieved scaling in refrigerant (vapour) with assistance with warm water or heater blanket charging of unit would be easy via suction shroeder port of compressor

  15. #15
    Join Date
    Mar 2009
    Location
    Mancheser
    Age
    41
    Posts
    55
    Rep Power
    16

    Re: What was I doing wrong

    Quote Originally Posted by thebigcheese View Post
    was it reclaimed r22 you where using
    Yes, Dont worry.

    Quote Originally Posted by El Padre View Post
    You can normally find a warm place to put the refrigerant cylinder before you commence the repairs, will save you loads of time.

    Cheers
    Yes I warmed the bottle in the site workshop with a heater prior to charging.

    Quote Originally Posted by kkeithd2 View Post
    Only 50 grams of liquid at 4 degrees r u sure you pulled a good vac on the system ?
    Yes I vaccd it twice and broke with ofn in between to below 2 torr both times to ensure no moisture present.

    Quote Originally Posted by frosty74 View Post
    always ensure you pull a good vac
    as previously mensioned warm the bottle tub of hot water you can also get heater jackets.

    I will have to try this.

    you can also charge liquid does your manifold have a sight glass?
    if so you can liquid charge very carefully flashing off through your manifold that can be a faster method also
    Sorry I didnt explain correctly, I did charge as a liquid boiling off in my manifold into the suction shroeder just before the comp inlet at around 2 bar.

  16. #16
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: What was I doing wrong

    Quote Originally Posted by lees8110 View Post
    Hi all,

    I am still very new to the trade and still have alot to learn.

    I am just after a bit of advice.

    I replaced a compressor the other day on a heat pump unit, the system is on R22 and requires a charge of 5.44kg.

    I decided to way the charge in as its a package unit, I trickle charged it into the suction as a liquid not exceeding 2.5 bar.

    I noticed the compressor was getting very hot although the the suction was nicely frosted. As though it wasnt getting enough cooling from the charge in. and then it went out on thermal.

    Now fully charged the system seems to be running fine and am getting all the correct temps/pressures.

    Could this of been down to the change over valve in the wrong position. Ie not in cooling mode???

    Thanks in advance for any advice given.
    Getting back to your question....it sounds like there is nothing wrong, except you might have taken a little too long putting the gas in the system.

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  17. #17
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: What was I doing wrong

    Quote Originally Posted by lees8110 View Post
    Yes, Dont worry.



    Yes I warmed the bottle in the site workshop with a heater prior to charging.


    Also when reclaiming it helps to use a cool bottle. I saw a bloke leave one in a freezer cold room on site before using it.
    Some recovery units have a diagram on the side with different ways of recovering refrigerant.
    Health and safety first..........unless I'm in a hurry.

  18. #18
    Join Date
    Jun 2009
    Location
    Columbus Ohio
    Age
    55
    Posts
    169
    Rep Power
    15

    Re: What was I doing wrong

    my reclaimer has a sub cool function.. on larger systems i reclaim for a while then hit the subcool function and that will make a bottle frosty for recovering if i want it to, but if im going to re-use the gas I dont get my bottle too cold...

    I also never re-use refrigerant from a fried compressor replacement, esp if it was an electrical failure.. I like to flush a system after compressor failure and use fresh gas.. might cost the customer a few more bucks but increases the longevity of the system.
    -Christopher

Similar Threads

  1. Can someone point what's wrong
    By Peter_1 in forum Industrial
    Replies: 30
    Last Post: 22-04-2008, 07:04 PM
  2. Wrong expansion valve installed
    By kentbf in forum Trouble Shooting
    Replies: 29
    Last Post: 02-03-2008, 08:49 PM
  3. Electronic controller probes wired wrong
    By Electrocoolman in forum Trouble Shooting
    Replies: 3
    Last Post: 12-11-2007, 06:39 PM
  4. Whats gone wrong!!!!!
    By jbear in forum Transport
    Replies: 2
    Last Post: 14-03-2005, 12:17 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •