    We are going to be re-equipping a freezer room although the equipment the supplier has quoted seems rather large. the internal room size is 3000w 2600 l and 2100h (mm). we have been quoted a 5 hp condensing unit, 2099watts and a 4.63 kw evaporator the pipe run is approx 15m. the only details i have of the previous equipment that was in the room is that it was a 2.5hp compressor. room is designed to sit at -21 deg c, all products are entering room frozen and room is for high usage, door leading into freezer room is off a coldroom which sits at approx 3 deg c. Does anyone think this is the correct equipment quoted



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: freezer room equipment

    What do the design calculations give you for the equipment size?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: freezer room equipment

    It looks Ok.

    Is it hermtic or semi hermetic compressor?

    Capacity is at -25°C evaporation temp.

  4. #4
    sharonzhang's Avatar
    sharonzhang Guest

    Wink Re: freezer room equipment

    Dear Jack,


    I am Sharon Zhang from Hongyi Precision Industrial Inc. We are manufacturer of digital temperature controller,digital thermometer. I think installer of cold room,like you, may have some needs of temperature controller in near future. Pls feel free to contact me at zzhy@hongyiinc.com if there is any need in future. Thank you so much!







    Quote Originally Posted by jack smith View Post
    We are going to be re-equipping a freezer room although the equipment the supplier has quoted seems rather large. the internal room size is 3000w 2600 l and 2100h (mm). we have been quoted a 5 hp condensing unit, 2099watts and a 4.63 kw evaporator the pipe run is approx 15m. the only details i have of the previous equipment that was in the room is that it was a 2.5hp compressor. room is designed to sit at -21 deg c, all products are entering room frozen and room is for high usage, door leading into freezer room is off a coldroom which sits at approx 3 deg c. Does anyone think this is the correct equipment quoted

  5. #5
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: freezer room equipment

    Sounds a bit over the top for a room that size with pre frozen product and entry from chiller area.
    More details on construction would help, ambient conditions etc.,
    The upside is that if oversized it will not run that much and be a power saver.
    magoo

Similar Threads

  1. Maneurop MT51HK4A - Freezer Room
    By Hatchy in forum Trouble Shooting
    Replies: 35
    Last Post: 09-08-2010, 12:10 PM
  2. Cold room/ Freezer combo.
    By dogma in forum Commercial
    Replies: 14
    Last Post: 09-11-2008, 02:25 PM
  3. Heat transfer coefficient - Coolpack
    By Graham in forum Fundamentals
    Replies: 10
    Last Post: 28-05-2008, 01:08 AM
  4. Freezer Room Panels
    By Feeze in forum Technical Discussions
    Replies: 10
    Last Post: 22-04-2005, 05:58 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •