    I am a new member, I have enjoyed reading the forums, so I decided to join your refrigeration family.

    I have a small problem with a split system that I am installing for a client. This air conditioner is a used unit.
    The problem that I am having trouble solving is that the condenser fan on the condensing unit will not close down. When the room temperature is reached and the compressor closes down the condenser fan continues to operate. Every thing else seems to be working ok.
    The Unit is an LG split system Model LV-B 2460 HS.
    I would be grateful if some one can make some suggestions.
    Regards Aussie



  2. #2
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Aussie

    hi ausie, sounds like the cond, fanis wired up wrong ,wire thw fan live onto the supply to the compressor then they both come on and go off together

  3. #3
    Join Date
    Oct 2008
    Location
    Australia
    Posts
    210
    Rep Power
    16

    Re: Aussie

    Or the relay is stuck on the pc board.

  4. #4
    Join Date
    Jul 2006
    Location
    Australia
    Age
    52
    Posts
    28
    Rep Power
    0

    Re: Aussie

    dose the condensor fan got contactor if dose could be welded in

  5. #5
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Aussie

    i think with those units, the condenser fan motor is switched via the indoor printed circuit board. Sounds like th relay iss latched on the indoor board.

  6. #6
    Join Date
    Apr 2008
    Location
    UK
    Posts
    215
    Rep Power
    17

    Re: Aussie

    Had a similar problem with an LG split a few years ago, the fan relay contacts were fused. When i rang for a replacement, the supplier said that it was a common fault on that unit, too long ago to remember the model no. though..

    Can u check the wiring diag Aussie to see where fan is powered from ?

  7. #7
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Aussie

    Does the outdoor fan run all the time, like if you left the unit unpowered for a while, then switched the power back on, does the outdoor fan start straight away? (possible miswiring or fully welded relay contacts - check the relay contacts on the PCB solder points to see if they are a closed circuit as it should be normally open, and recheck your wiring).
    If not, if you switched it to cooling and ran it for a few minutes and switched it off, does the fan stop? (if so possible sticking relay that only sticks when running for a few hours).

    I would say troubleshoot/replace the relay first, but being it's an LG, the indoor PCB is only going to be about $60 as LG parts are so cheap, so just get a new indoor PCB if it seems the PCB mounted relay is playing up.

Similar Threads

  1. Only an Aussie could pull this one off!!
    By tonto33 in forum Chit Chat & Service Stories
    Replies: 0
    Last Post: 23-12-2008, 05:28 PM
  2. Aussie Split Install
    By FreezerGeezer in forum Air Conditioning
    Replies: 24
    Last Post: 03-08-2007, 12:07 AM
  3. Aussie Qualifications
    By colinmcmanus in forum Chit Chat & Service Stories
    Replies: 2
    Last Post: 27-10-2006, 06:26 AM
  4. Simply an Aussie Lady needing advice
    By clearlipstick in forum Fundamentals
    Replies: 27
    Last Post: 17-12-2005, 03:27 PM
  5. Aussie do it tough
    By Greg W in forum Air Conditioning
    Replies: 8
    Last Post: 29-09-2005, 06:45 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •