15-02-2005, 05:54 PM #1
Burst Coil
One of our controls specialists that we use has just rang for a bit of advice.
He's got a job with a heat pump on and he's written the software for defrost (as advised by the client - We*the*ite) (not to mention any names) as follows:
1 When the coil temperature reaches 0degC then the reversing valve changes over for a period of 8 minutes or until the coil reaches 60deg C
2 After a defrost the system goes into a 20 minute anti cycle stage and does not run.
3 If the coil drops to 0degC during the anti cycle time then it must defrost again before going back into normal heating mode.
The system was commissioned by Wea*her*te in July but they have just rang our engineer mate and said that the system has failed with a burst coil due to the defrost software being incorrect and saying that he must stand the cost of the repairs!
Any thoughts??
Apparently, the coil sensor is on the "pipe just before the compressor" and only the first bottom 1/4 of the coil ices up
Among other things my first opinion was that if the software was written to the clients instructions and tested to comply then the refrig eng who commissioned the system must have been happy with the software at that time as he's signed off the commissioning for the system. Who do you think is right?
Similar Threads
-
Why a capacitor on contactor coil
By wambat in forum ElectricalReplies: 18Last Post: 15-05-2009, 03:18 AM -
Evaporative Condenser in reverse cycle
By Friobernal in forum IndustrialReplies: 6Last Post: 16-04-2009, 02:06 PM -
Indoor coil capacity?
By Larry2 in forum Air ConditioningReplies: 2Last Post: 23-07-2006, 01:47 AM -
Coil design?
By The MG Pony in forum FundamentalsReplies: 4Last Post: 20-06-2006, 12:32 AM -
Article in ACH&R News
By Gary in forum FundamentalsReplies: 8Last Post: 20-05-2003, 12:27 AM